6/3 romex

  1. Shonn

    Hot tub wiring with 6/3

    I will be getting a new spa with 4 wire connection. I have existing 6/3 wiring to the location. 6/3 goes from service panel 50am to far end of house 50amp gfci breaker box for spa then through conduit to spa. Question 1 is I'm assuming I can use the bare ground as ground plus it's smaller...
  2. SEEKING_HELP

    EV CHARGER

    Running new line of 6/3 cable from main to garage to charge electric vehicle. OK to put the 6/3 cable through 1" pvc pipe over ceiling in finished basement? Concerned about heat from 6/3 cable running 40amps. Will use 50A GFCI.
  3. chinna na

    NM 6/3 wire from main panel to NEMA 14-50 socket 1 foot away.

    Gentleman, Trying to install a NEMA 14-50 socket for electric vehicle charging near the main panel inside garage. Trying to install everything as per code and pass inspection. The closest location is about a foot away from main panel. I installed the 50AMP breaker in the lowest position in...