  1. Cool Blue Harley

    Is this wet vent of a toilet OK? Theoretical.

    IAPMO (International Association of Plumbing and Mechanical Officials) is responsible for the compilation and publication of the Uniform Plumbing Code. For a better understanding of of the actual meaning behind each code section, you can visit their website and access the Illustrated Training...
  2. Cool Blue Harley

    Is this wet vent of a toilet OK? Theoretical.

    The code section I am referencing is UPC 908.2 “HORIZONTAL Wet Venting for Bathroom Groups”
  3. Cool Blue Harley

    Is this wet vent of a toilet OK? Theoretical.

    The configuration of the horizontal wet vented WC in the OP is both non-code compliant and substandard in design, thus performance. Horizontal wet venting is exactly as it sounds. All of the connections are made laterally, on the horizontal. It’s similar to a combination waste and vent system...
  4. Cool Blue Harley

    Is this wet vent of a toilet OK? Theoretical.

    Reach4. Your diagram as illustrated would not pass inspection in California which follows the UPC. The WC is not vented in an approved manner. Section 905.2 allows venting to be installed in a horizontal position. However, the invert of the vent connection must be above the centerline of the...
  5. Cool Blue Harley

    180 degree turn in toilet drain pipe

    Why not schedule a reinspection to confirm that the reconfigured piping is up to code? You mentioned that the bathroom is on the second floor. Is there a floor above?
  6. Cool Blue Harley

    180 degree turn in toilet drain pipe

    You are going to have nothing but headaches and problems down the road from your unpermitted bathroom remodel.
  7. Cool Blue Harley

    Help identify brand cast backwater valve

    Yes. They are available in numerous supply houses in SF. But the post by Reach4, #3 of this thread, is spot on. Why spend time and money repairing a backwater valve of poor design. Reach is referring to the Mainline backwater valve which is always open, unless a back flow situation occurs. I...
  8. Cool Blue Harley

    How do You pronounce "potable" ?

    How do you pronounce notable?
  9. Cool Blue Harley

    Plumbing Company Names

    Pune Tang Plumbing
  10. Cool Blue Harley

    Street elbow

    They are allowed on a fuel gas system, as are bushings, nipples, unions, etc. As long as the piping is exposed. They are not allowed on concealed fuel gas piping. On concealed fuel gas piping, the code specifically limits the fittings used to: elbows, tees, couplings, and right/left...
  11. Cool Blue Harley

    Reusing threaded pipe

    You are correct. The tapers oppose each other.
  12. Cool Blue Harley

    Plumbing code question for cleanout

    If inspector #2 wants to wordsmith, you should refer to the code book. CA Plumbing Code: Chapter 2, Definitions, Trap Arm. That portion of a fixture drain between a trap and the vent. By placing your C.O. where you did, you have met the letter of the code exactly as it was ment to be...
  13. Cool Blue Harley

    Plumbing code question for cleanout

    California Code Building Drain: That part of the lowest piping of a drainage system that receives the discharge from soil, waste, and other drainage pipes inside the walls of the building and conveys it to the buildings sewer beginning 2 feet outside the building wall. You stated that the...
  14. Cool Blue Harley

    No washing machine standpipe vent?

    Homes were plumbed that way everywhere in the 60’s and 70’. And perfectly to code at the time. The clothes washer standpipe does not need a trap or vent because it discharges indirectly into the floor drain tailpiece, upstream of the trap. It’s clearly visible in your second photo. It’s the...
  15. Cool Blue Harley

    Trap arms and bends before you need a cleanout.

    Not to exceed 90 degrees of change on a trap arm without a cleanout. Does not apply to vents.
  16. Cool Blue Harley

    Washing Machine Vent Distances

    The UPC table for maximum length of drainage venting is 703.2. The maximun horizontal length is chapter 9, section 904.2.
  17. Cool Blue Harley

    Would this vent configuration work?

    Don’t know IRC. Here we use UPC, superseded by state and then local amendments. Structural conditions on larger jobs are generally limited to underground piping where mat slab, grade beam, or distances from walls prohibit continuous venting. Once out of the ground, it’s straight up because...
Top
Hey, wait a minute.

This is awkward, but...

It looks like you're using an ad blocker. We get it, but (1) terrylove.com can't live without ads, and (2) ad blockers can cause issues with videos and comments. If you'd like to support the site, please allow ads.

If any particular ad is your REASON for blocking ads, please let us know. We might be able to do something about it. Thanks.
I've Disabled AdBlock    No Thanks