    Thanks Speedy Petey for the concerns. The tank alert is an SJE 101 series built in 1996. As far as I can tell the line that runs to the float is 12 volts. The use of UF wire was advised by several people. Seems in Mn, even if it is in a conduit it has to be rated for underground use. My...
  2. R

    Septic system electrical lines

    Thanks guys, The float alarm sets off an audible signal in the house. I did contact a local electrician yesterday and he advised me that they could both go in the same conduit. I will use a 12-2 UF line for both even though he said I could use 14-2. I can get 250 feet of the 12-2 cheaper than...
  3. R

    Septic system electrical lines

    Thanks, HJ! I appreciate the help.
  4. R

    Septic system electrical lines

    When my mound septic system was installed about 15 years ago the electrical lines for the septic pump and alarm were both just buried about a foot underground. Recently one of the great Minnesota gophers chewed through the main power cord and it shorted so bad I couldn't get the breaker to stay...