    Consequences of removing basement heat exchangers on a FHW system?

    System is running much better... Thanks jadnashua. I bumped the low temp on the control to 180°F and left the high limit at 200°F, maintaining the 20° differential required on the warning label. Now the system gets the house up to temperature much quicker. The circulator and burner rarely...
  2. BLAAT!

    Consequences of removing basement heat exchangers on a FHW system?

    Okay... so I did some more research and thinking. Thanks for the suggestion of not taking things apart. I now realize that the boiler is probably adequate to heat the whole house including the basement. Something else was the problem. I discovered that the pressure in the system was only about...
  3. BLAAT!

    Consequences of removing basement heat exchangers on a FHW system?

    Thanks jadnashua. How do I measure the supply and return temps? A thermocouple on the surface of each pipe, or do I need to measure the temp of the actual water flowing through by tapping the pipe somehow? Do you know if there is there a practical convention for measuring this? The boiler...
  4. BLAAT!

    Consequences of removing basement heat exchangers on a FHW system?

    Hi All, I recently purchased an 1800 square foot house built in 1950 with a FHW by oil system that takes an extremely long time to get up to temperature... like 3-4 hours or more. The house has one single zone/loop. The radiators on the upper floors never really seem to get hot, just warm, even...