    Is there a 200 amp breaker box with 100 amp main

    I don't know about it where you are. But I just recently replaced my main panel as well as the separate service I had for my garage. I bought 2 new panels. one is a 100 A the other a 200A on looking up the specs of the panels. the 100a is rated higher then they are breakered for. . the 100A is...
  2. cswilson

    Question about Outlets and terminals/push-in(real question, not a troll)

    Is it allowable to use BOTH screw and push-in's on the same receptical? My situation is this, I have 3x 14/2 romex running into a 12.5ci (2"x3"x2.5") box. the Ontario electrical code allows 6 conductors and 0 or 1 marret in that size of box. If I can use both screw terminals and 1 push in I...