    problem filling hydronic weil mclain system

    Problem Resolved Thanks for all the suggestions - my problem was identifying the fill valve behind and under the expansion tank. I removed the internal valve mechanism and was able to fill normally - now I have to find an appropriate replacement. The flo-control valve was a non-issue...
  2. J

    problem filling hydronic weil mclain system

    Thanks for the suggestion. There are two in-line valves for filling, and both operate properly. The system has a "flo-control" valve (B&G) SA-1 1/4 which I gather is to prevent hot water circulation when the circulator pump is not running. Is this the valve you are referencing? Do I...
  3. J

    problem filling hydronic weil mclain system

    Thanks for the reply - but i do not know what an air scoop is or how it operates. How can i identify it?
  4. J

    problem filling hydronic weil mclain system

    My son recently bought an older house with weil mclain gas fired boiler and baseboard heat. The system had been drained. We tried filling the system using city water and could not complete the fill - some air came out of the bleeders, but then quit, and no water was seen. All valves are...