    Just a thought make sure you use the voltage setting on the meter and not the continuity (ohms/resistance) setting. You would burn your meter up at the very least and could cause the battery to explode.
  2. CodeOne

    Wiring my shed with 10-3

    Maybe he was thinking about a subpanel feeding swimming pool equipment or a panel or disconnect feeding equipment on artificial or natural bodies of water, which does require an insulated ground in the 2008 nec. Articles 680 and 682 respectively.
  3. CodeOne

    Outdoor sub-panel for pool

    How deep is this above ground pool?
  4. CodeOne

    Outdoor sub-panel for pool

    680.25 Feeders. These provisions shall apply to any feeder on the supply side of panelboards supplying branch circuits for pool equipment covered in Part II of this article and on the load side of the service equipment or the source of a separately derived system. (B) Grounding. An...
  5. CodeOne

    Derating for number of conductors in conduit

    TW is rated for 25 A in the 60 degree column. #12 is limited elsewhere in the code to 20 A. You would only have a problem if you had TW running in the pipe with the THHN/THWN conductors due to the fact the TW would have to be derated from the 60 degree colum. The TW insulation cannot handle the...
  6. CodeOne

    Derating for number of conductors in conduit

    You use the 90 degree column from table 310.16 for your derating. #12 is good for 30 amp in the 90 degree column. So it would be 30 x 70% = 21Amp you can use a 20 a breaker. A larger conduit does not circumvent the need for derating.
  7. CodeOne

    Wiring for boat lift motor

    NM cable nor UF cable are approved for use on at or going to boat docks! Call an electrician!
  8. CodeOne

    New exterior receptacle in old brick wall

    Your finished product would look like this
  9. CodeOne

    New exterior receptacle in old brick wall

    This is a box by arlington Ive had excellent sucess chipping out mortar and one brick and installing in the brick.
  10. CodeOne

    electrial for new disposal hookup

    No What you are talking about doing would not be code compliant!
  11. CodeOne

    Can "any" schedule 80 PVC be used as electrical conduit...

    Sorry been gone for a couple of days. Yes that looks like SER cable. Not sure about the area you were trying to go around for boxing. I was speaking of framing out the area and covering with drywall. Yes you do need a cable clamp.The 6' needs to be the distance apart, if you turn a cornor you...
  12. CodeOne

    Replacing Washer outlet with dual receptacle

    Is there a laundry tub within 6' of this rec? A 15 A duplex is ok on a 20A cir. which gfci's are.
  13. CodeOne

    Crimping ground wires in an outlet box

    Twist your groundg together for approx 3" (best to go past face of box), slide crimp on , crimp , leave about 3" out of crimp to attach to your devices.
  14. CodeOne

    Can "any" schedule 80 PVC be used as electrical conduit...

    I would personally use SER cable, no pipe needed! Yuo would need a cable clamp at the box per Article 312.5(C). Also you could frame a small chase to protect the wire. Who is doing the work you stated you didnt do the framing being paralyzed or was that temp.? In NC you have to be liscened to...
  15. CodeOne

    Premature lamp burnout

    Take the recessed can down and check the junctions in the j-box, espically the neutral connections. If you have one that is not made up properly they have been known to blow bulbs with spikes.
  16. CodeOne

    Can "any" schedule 80 PVC be used as electrical conduit...

    If you are talking about caulking, it would probably be better to use Duct Seal putty.
  17. CodeOne

    Keep Buying DIY Books

    Quote from one site with the story. "On the one hand, the implications could be far-reaching," he said. "Home repair is one of those things that you can't learn out of a book. You need to be trained by an expert." However, he noted, "the codes have changed a great deal, and the enforcement...
  18. CodeOne

    Will two Taco timers work in parallel?

    What is the second timer for? Why would you bypass the aquastat with your second timer? Are these timers mechanical or electronic?