    Thank you gents for all the helpful info.
  2. D

    Attic Bathroom Plumbing

    this is a view of the vent that steps up in relation to the crown weir. I am doing this bathroom myself, I am more concerned about it being fully functional and not give me problems down the road than passing an inspection. Thank you gents for pointing me in the right direction.
  3. D

    Attic Bathroom Plumbing

    mass UPC The allowed developed length from shower trap to vent per UPC (Applied Plumbing Code in Mass) is 8 FT which I don't have. So the fact that the wye combo is not horizontal, but rotated with almost 45 degrees upward does not help. Then I will have to make the shower smaller and bring...
  4. D

    Attic Bathroom Plumbing

    Can I completely remove the shower vent? Is it better with this horizontal run or without it? Do you see anything else wrong with this bathroom drains?
  5. D

    Attic Bathroom Plumbing

    I hope I got it right. Once I am done, I will have to test the drain line, should I do a pressure test or a water test? If pressure test, is there any kit I can buy?
  6. D

    Attic Bathroom Plumbing

    Correct, there will be a wall that I have not updated in the plans. I installed the vent up into the wall. However, I had to offset it from the drain line to the wall using a wye combo on 45 degrees+45 degree bend and a 90 elbow. this was the only way I could get it to the wall without drilling...
  7. D

    Attic Bathroom Plumbing

    thank you Jeff for all the good info. I think I have to add the vent to the shower since all the vent pipes will tie into the existing vent on the wall on the right ( that round white circle) and this run is longer than 6 ft.
  8. D

    Attic Bathroom Plumbing

    The magenta line is the vent that runs horizontal only about 2-3 inches above the shower drain until it reaches the wall on the right.
  9. D

    Attic Bathroom Plumbing

    Jeff, all the blu lines represent a 2" pipe which will have a 1/4" slope for the trap arm. from the wye combo to the 3" pvc drain (orange line) it will have a 3/16" slope for 5'-4" distance.7, then the slope becomes again 1/4" for the 3" drain ( in orange) that connects the toilet with the main...
  10. D

    Attic Bathroom Plumbing

    I have updated the plans a bit after looking at the joist configuration. I have eliminated the toilet vent. the shower pan is 40" x 48", probably the sketch is deceiving. My concern is regarding the 2" drain going thru the 2x7" joists. Distance from CL of shower drain to 3" main( 3x3x2 combo in...
  11. D

    Attic Bathroom Plumbing

    I am adding a bathroom to the attic and have been working with the plans to get the plumbing done. Below I have attached a sketch showing the fixtures. The existing main stack of the 2 floors below is right below the toilet, but I can not add a 3" main stack there as there is no room. I have to...