  1. kalex1114

    Why do mod-con boilers even need an offset setting?

    Hi @Leon82 we meet again :) I may adjust the ramp settings. I noticed it too that even though its 66-67 its still comfortable since heat is running constantly
  2. kalex1114

    Why do mod-con boilers even need an offset setting?

    @justcallmeglen - KHN is similar to WHN . I thought about doing that but I might have to adjust it for cold snaps. I did load calcs and adjusted my water temps based on the recommendations. 145f at 7f and 105f at 68f. But i did run into an issue with master suite. When we had a cold snap...
  3. kalex1114

    Why do mod-con boilers even need an offset setting?

    DW what model is your lochinvar? I have KHN-110. Offset is there in order for the boiler not to cycle. My boiler seems to behave different from yours. It overshoots often and can't adjust its firing rate in drastic moves. I have an offset of 10f and it does help in my case. As an example...