Search results

  1. RKP

    Adding Economizer to GV90+4

    Yes, the boiler is in an unfinished full basement.
  2. RKP

    Adding Economizer to GV90+4

    60,000 BTU x 1.4 = 84,000 BTU which is output of the new boiler.
  3. RKP

    Adding Economizer to GV90+4

    Fin tube is emitting approx 25,000-30,000 BTU/hr per zone/floor, plus whatever the indirect hot water pulls. Gas bill analysis also came out to ~60,000 BTU/hr. House is 17 year old construction, with no upgrades to the original construction, 2,500 sq ft.
  4. RKP

    Adding Economizer to GV90+4

    I recently had a GV90+4 installed. It was somewhat of a winter emergency as my old Burnham boiler had started leaking and it was discovered that the cast iron portion was disintegrating. I tried my best using fin tube measurements and old heating bills to downsize the boiler, since the plumber...
Top
Hey, wait a minute.

This is awkward, but...

It looks like you're using an ad blocker. We get it, but (1) terrylove.com can't live without ads, and (2) ad blockers can cause issues with videos and comments. If you'd like to support the site, please allow ads.

If any particular ad is your REASON for blocking ads, please let us know. We might be able to do something about it. Thanks.
I've Disabled AdBlock    No Thanks