Follow up to this - had a well recommended company come out to check out the system. They pointed out the low F output and low dT on the return...
Thanks again Dana. I have a company that does hydronics coming out next week to give me their thoughts, though I am leaning towards doing the...
It's straight shot, so to speak - supply side is 1 1/4 copper out of the boiler and the return is...well another 1 1/4 pipe that is fed from a run...
My multimeter has a tape on thermistor probe. I that used to measure the return temp - I shot the temp gun against the black duct tape I used to...
Thanks again, both to Dana and Fitter30 for answering my questions. Looks like I'll be insulating a wall this spring at the minimum, and looking...
It's a taco 007-F5. As for loops...each room/hallway/area has it own loop. I think. The manifold in the basement has 18 valves that correspond to...
Dana - thanks for taking the time to respond. And yes, I was using 65F as the base temp. HDT was 12, as you indicated. Basement is semi-finished,...
Boiler runs at 120. There's copper tubes in the embedded in the ceilings of the house - essentially making the ceilings radiant panels.
Background - Cincinnati Ohio - 1.5 story cape cod, built in 1951. Brick on block construction, minimal (rockwool) insulation in the knee-wall...