Pressure regulating valve

Users who are viewing this thread

HBM

New Member
Messages
7
Reaction score
0
Points
1
Location
Virginia
I have had my PRV fail twice in a 2 year period. I believe it is a Wilkins 1 inch 600xl. My question....is there something that is causing premature failure? Is this typical or perhaps I got a lemon? Rebuild kit has fixed it both times.

My thoughts are perhaps debris since new houses are going in nearby (didn't see anything when I rebuilt it)

The pressure at the street is high at 150psi. City water that is pretty hard at 15gpg
 

HBM

New Member
Messages
7
Reaction score
0
Points
1
Location
Virginia
Can you place a wye strainer prior to the PRV to help catch sediment?

I forgot to mention it does have a strainer built into the prv but it always appeared clean. Also I use about 5000 gallons Of water per month.
 

Breplum

Licensed plumbing contractor
Messages
1,956
Reaction score
793
Points
113
Location
San Francisco Bay Area
Being a model with a strainer, that is certainly very abnormal.
I've had defects out of the box, but it is certainly very peculiar.
Nice that rebuild kits worked. I've not had rebuild luck on several 1.25" and 2" of the 600XL and 70XL. That's why I love double union 70XL

zurn-70xl-double-union.jpg
 

Dj2

In the Trades
Messages
2,611
Reaction score
258
Points
83
Location
California
I would give Wilkins a call, as this is not what you may expect from their PRVs.
 