ghaun
Member
Dry vents need to be "vertical" from their takeoff to 6" above the flood rim level of the fixture served. Likewise when you connect dry vents, the connection needs to be 6" above the flood rim level of any of the fixtures being dry vented.
Cheers, Wayne
View attachment 72433
Wayne, thank you.
So, I thought that once the wet-vent portion of a horizontal wet-vented bath went vertical, it could not go horizontal again. Is that not the case?