I just did a water heater flush at my rental house today, and had the tenant open the hot water at the sink.

but the wh was still draining really slowly, until I opened the tp valve, and the water finally started gushing out.

I kept the tp valve open for 30 minutes while i was flushing and draining.

any harm in doing it like this every year?


I don't know why there was still a vacuum even with the sink faucet turned on.
the wh is on a platform and the drain valve is about waist height.
 

Sylvan

Still learning
Messages
2,757
Reaction score
689
Points
113
Location
New York
"
I don't know why there was still a vacuum even with the sink faucet turned on.
the wh is on a platform and the drain valve is about waist height."

Take a take a large bottle and turn it upside side down and you will see the liquid go plop, plop, plop STARVING for air

Now place a small hole on the opposite side and the liquid will flow faster ax now your not creating a vacuum lock

On high rise buildings when the unknowing open a valve in the basement and do not have a vacuum relief valve by a tank 40 stories up the tank will implode

The NBBI and ASME all suggest to test the T&P at least once a year some codes suggest more often

Actually the "Blowdown valve" located o the bottom of the tank should be opened at least once a year to get sediment out of the bottom of the tank so it will not hinder the efficiency of the heater.

The sediment and mineral deposits act like an insulator

index.php
 
Last edited by a moderator:

Phog

Active Member
Messages
454
Reaction score
84
Points
28
Location
Rochester NY
The heat trap device inside the water heater connection nipple could be restricting things. Nothing wrong with using the T&P like you describe except for the possibility that you're sucking debris into it & it might fail to seal afterward. You could probably cure that by blowing some water out of it after the flush (with tank under pressure). You could also try using a faucet in the cold water plumbing as air inlet instead of the hot faucet. The way the heat trap nipples work is different between the hot and cold lines & the cold might work where the hot didn't.
 

Reach4

Well-Known Member
Messages
38,795
Reaction score
4,413
Points
113
Location
IL
Nothing wrong with using the T&P like you describe except for the possibility that you're sucking debris into it & it might fail to seal afterward.
That would be a bonus reason to use the T&P valve. It is much better to find that the T&P valve sticks while you are doing maintenance than to have it happen when you don't notice. That is why tests are recommended: does it open, and will it close back?
 

Pman6

Member
Messages
78
Reaction score
1
Points
8
Location
Los Angeles
The heat trap device inside the water heater connection nipple could be restricting things. Nothing wrong with using the T&P like you describe except for the possibility that you're sucking debris into it & it might fail to seal afterward. You could probably cure that by blowing some water out of it after the flush (with tank under pressure). You could also try using a faucet in the cold water plumbing as air inlet instead of the hot faucet. The way the heat trap nipples work is different between the hot and cold lines & the cold might work where the hot didn't.


this is a bradford white wh.

debris... oh is that why the internet discourages using the tp valve to drain the w.h?

The tp valve is at the very top of the w.h, so if i drain the water a little from the bottom and then open the tp valve, it should not suck in deposits.


as for the w.h draining slowly, i'm pretty sure the opened kitchen faucet was higher than the w.h drain valve, so i expected the wh would drain faster.
 

Phog

Active Member
Messages
454
Reaction score
84
Points
28
Location
Rochester NY
The tp valve is at the very top of the w.h, so if i drain the water a little from the bottom and then open the tp valve, it should not suck in deposits.

Debris getting sucked into the T+P valve would be more like cobwebs and whatever else is inside the external discharge tube. Not stuff already inside the tank.

Whether an open faucet is higher or lower than the tank would have little to no effect on allowing air inlet during a drain/flush.

By the way, many people flush the tank under pressure -- just attach a hose to the drain cock, run the other end into a sink or other drain, and let 'er rip. The pressure can help force out sediment. (Many schools of thought on this way vs. turning off the supply, I have no opinion on which way is "better")
 