Septic Tank Water Tight Test

Users who are viewing this thread

Jazzman

Member
Messages
48
Reaction score
0
Points
6
Location
Oregon City
I’m in the process of replacing septic tank and drain field. One of the requirements is a water tight test on tank. You’re required to fill tank 2” above riser and hold water for 24 hours. Then you call for inspection. I’m having trouble figuring out how you seal inlet and outlet pipes on tank. Is there anything other than installing 4 4” plugs in both pipes? It seems like it would be difficult to reach down through riser and and access bottom of both pipes. Is there some kind of balloon you could inflate that would seal tank tee?

Thanks
 

Reach4

Well-Known Member
Messages
38,892
Reaction score
4,434
Points
113
Location
IL
Cherne test ball with an extension to let you put in or take out air at a short distance.

black-cherne-rubber-fittings-270040-40_145.jpg
black-cherne-shower-hoses-274011-64_145.jpg


For that tee,
black-cherne-rubber-fittings-271047-64_145.jpg
the Cherne 271047 looks good to me.
 