Warm water delivered to cold supply lines

Users who are viewing this thread

BigEdgar

Member
Messages
48
Reaction score
5
Points
8
Location
Seattle
Hello,

I'm having an issue with warm water being delivered to a cold water fixture. Our water heater is in the basement. When I turn on the cold sink faucet in the 2nd floor bathroom, we get about 5 seconds of cold water, followed by about 15 seconds of warm water (85 degrees) and then we get cold water again (50 degrees). I suspect it could be hot water from the water heater backfilling into our cold supply lines.

Here are some notes and things I've investigated:
  1. The cold water supply lines in the basement leading up to the water heater are warm to the touch. The main lines are copper and it's less evident there, but the supply lines that tee off the main to lead to the 2nd floor supply are PEX - you can feel the heat more clearly when touching the PEX.

  2. I've insulated the pipes around where hot and cold supply lines cross to rule out the hot water pipes heating the cold. This didn't solve the problem.

  3. We've had this same plumbing setup for the last 14 years and this issue only started appearing in the last 6 months.

  4. This issue was present during the summer when we don't use heat (forced air), so it's not related to something like pipes being near a heat vent.

  5. I can't really replicate this situation in other fixtures in the house, perhaps because the other cold water supply lines are farther down the line from the water heater. It seems to be isolated to the 2nd floor bathroom, whose supply lines are closest to the water heater.

  6. The other cold water supply lines in the 2nd floor bathroom seem impacted as well (I measured water at 72 degrees from a sample of the toilet tank). So that rule out an issue with the sink fixture.
I've diagrammed the setup below in case it's helpful. I'd be grateful for any ideas on what might be going on, or other things that I could do to troubleshoot. Also, if there's any immediate danger with this situation, it'd be good to know that as well .

Thanks!

upload_2020-3-9_14-16-16.png
 

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,770
Reaction score
1,190
Points
113
Location
New England
Most water heaters were delivered with heat traps. IF yours was, and they were installed, the one on the cold line could have failed, and is allowing water to migrate up the cold line via convection.
 

BigEdgar

Member
Messages
48
Reaction score
5
Points
8
Location
Seattle
Well dang, that certainly would make sense. I didn't know that a heat trap was a thing. Here's a picture of the actual setup and the inlet (cold is on the right in the first picture). A few follow up questions on this:

  1. Would the heat trap be integrated into the nipple, and does that look replaceable based on the second picture below?
  2. A little bit of Internet research also seemed to indicate I could replace the copper flex line with something that I could make a loop out of. That seems like it could be easier than replacing the nipple, but is that a viable alternative?
Thank you!

IMG_20200309_160932.jpg
IMG_20200309_160910.jpg
 

Terry

The Plumbing Wizard
Staff member
Messages
29,942
Reaction score
3,459
Points
113
Location
Bothell, Washington
Website
terrylove.com
When there are heat traps, they're in the nipples.
I see some 75 gallon 1" nipples with flaps. The plastic balls they used to have would sometimes wind up floating downstream. What a mess that was.
I have an instant hot in the kitchen. That gives me a burst of warm water at the sink on the cold side.
 

BigEdgar

Member
Messages
48
Reaction score
5
Points
8
Location
Seattle
Thanks, Terry - we don't have any instant hots in our plumbing, so I'm leaning towards the heat trap failure being the likely culprit. Do you think a loop in the copper supply line would be a viable alternative to the mechanical heat trap in the nipple? Or will we have to replace the nipple / heat trap to fix?
 

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,770
Reaction score
1,190
Points
113
Location
New England
Having an inverted loop on the inlet piping if deep enough, should stop the convective loop.
 

BigEdgar

Member
Messages
48
Reaction score
5
Points
8
Location
Seattle
Thanks, Jim. I tried yesterday to get the nipple off to replace the nipple and heat trap. I knew there was a chance that I could wreck the nipple, and since this water heater is 14 years old, I decided I'd give it the old college try, but if I couldn't get it off I'd consider it a sign that it was time to get a new water heater. I put a 5/8ths inch bolt in the nipple to keep it from collapsing, but this is one of those nipples that's tough to grip without damaging the threads, so I bailed when I couldn't get it to turn and my plumber's wrench started to strip the threads on the nipple.

I put it all back together and will start looking for a new water heater (wife says I should look at tankless). Thanks again for the help - you guys are awesome!
 

Reach4

Well-Known Member
Messages
38,861
Reaction score
4,429
Points
113
Location
IL
  1. Does your big copper cold pipe above the thermal expansion tank feel warm? That would indicate this unwanted circulation.
  2. You have a ground bypass wire between your cold pipe and your gas pipe. That doesn't seem right, but I am not sure. Normally such a bypass is between the hot supply and cold supply. That is not causing your water temperature symptoms.
 

BigEdgar

Member
Messages
48
Reaction score
5
Points
8
Location
Seattle
Hi Reach4,
  1. Yes, the big copper cold pipe above the expansion tank is warm and it's backing up into the section that tees off to a pex line that goes to the 2nd floor bath, where this issue is most prevalent. I tried to show that in the diagram included in my first post.
  2. The ground bypass goes between from the gas pipe to the hot water and then to the cold water pipe. You can't see the connection to the hot water pipe in the photo, but it's there.
 

Reach4

Well-Known Member
Messages
38,861
Reaction score
4,429
Points
113
Location
IL
Yes, the big copper cold pipe above the expansion tank is warm and it's backing up into the section that tees off to a pex line that goes to the 2nd floor bath, where this issue is most prevalent. I tried to show that in the diagram included in my first post.
I had lost track of that diagram. A spring loaded check valve in series with the shut off valve in your diagram would stop that hot cold, but I think that would be hard to pipe in.
 

BigEdgar

Member
Messages
48
Reaction score
5
Points
8
Location
Seattle
Hmm... The spring loaded check valve is an interesting idea. It would be easy to install one on the end of the flex copper line that feeds the WH, but I'm betting that it's not safe to install the check valve between the WH and the expansion tank on the cold side (city water / rest of cold system --> check valve --> expansion tank --> WH).
 

Reach4

Well-Known Member
Messages
38,861
Reaction score
4,429
Points
113
Location
IL
but I'm betting that it's not safe to install the check valve between the WH and the expansion tank on the cold side (city water / rest of cold system --> check valve --> expansion tank --> WH).
You are right that the expansion tank must be on the WH side of the check valve. Click Inbox.
 

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,770
Reaction score
1,190
Points
113
Location
New England
Probably the easiest thing to try would be to get a longer flex pipe and run it in a loop. The extra pressure may slow the convection down. WIthout anything to stop the convection, it can work its way all the way up the pipes.

New WH will come with a check valve on both the hot and cold lines. Make sure to install them on the proper sides, or you'll not get water in or out!
 

BigEdgar

Member
Messages
48
Reaction score
5
Points
8
Location
Seattle
I know this thread is a few years old, but as the OP, I wanted to write back and update with the resolution in case others find this thread in the future and it is helpful. It turns out that the problem causing the hot water to circulate into the cold water pipes was actually at the 2nd floor shower in the mixing valve. I was surprised by this as it resulted in warm water backing up all the way from the second floor and into the basement (The issue was much more prominent at the second floor fixtures, but it's still felt warmer than it should have been in the basement) but that's what it was. I changed the mixing valve a few months ago and the problem is solved. Huge thanks to everyone on this forum for the helpful suggestions!
 
Top
Hey, wait a minute.

This is awkward, but...

It looks like you're using an ad blocker. We get it, but (1) terrylove.com can't live without ads, and (2) ad blockers can cause issues with videos and comments. If you'd like to support the site, please allow ads.

If any particular ad is your REASON for blocking ads, please let us know. We might be able to do something about it. Thanks.
I've Disabled AdBlock    No Thanks