I am in the process of designing a new well setup for our future home and hoped that I could get a sanity check on some of my numbers. I have lurked here for a while and appreciate the expertise and regional perspectives on this forum!
Well:
Approx 10 gpm (possibly a bit less in dry season)
6" steel casing to 18', bedrock to 250'
Static level 20'
Dynamic level 170'
Pessimistic dry year guess 200'
House:
130' elevation above well head
900' horizontal distance
Very rocky soil
I am looking at using 1-1/4" PVC sch40 or HDPE poly for the in-ground pipe and installing a 1.5HP 7gpm pump. The various calculators tell me that 1200' of pipe would add another ~15' head (plus some for fittings) and the water would travel at 1.8 fps in the pipe.
Adding in the 60psi for the house at high pressure, that would add roughly 140' head for a total of about 485 ft head. That converts to roughly 210 psi at the pump in a dry year:
200' well
130' elevation
15' friction
140' house @ 60psi
---
485' total head
Question 1: If I go to 1" pipe, the friction jumps from 15' to 43' of head. I haven't really added anything for fittings at this point. Does my choice of 1-1/4" seem about right?
Question 2: I would like to use HDPE black poly pipe in the well, since it would be easier to pull by hand. I had a reasonably positive experience pulling a previous poly well and think threading PVC sounds like a chore. However, it seems hard to find HDPE to handle 210 psi + safety margin. Should I just use Sch80 PVC in the well instead? Can anyone comment on handling thick-wall black poly?
Question 3: For the in-ground part, I don't mind gluing PVC but, with rocky soil, I am not sure if I should also use poly for that. Since the pressure is less from the well head upward, I think I can use 160psi or 200psi poly. We are in a seismic region and wasn't sure if poly might also handle shifting better than glued PVC? However, straightening hundreds of feet of stiff poly may be just as much work as gluing PVC.
Question 4: I like the idea of a CSV, but I am worried about increasing the back-pressure at the low end of the pipe. I think the pump could take it, but I don't know about putting even more pressure on poly drop-pipe. We are mostly a household of 2 (occasionally 4) and it looks like the CSV shines more in higher-demand situations. Thoughts?
Thanks again for any feedback. I have found a lot of the older threads here very educational.
Well:
Approx 10 gpm (possibly a bit less in dry season)
6" steel casing to 18', bedrock to 250'
Static level 20'
Dynamic level 170'
Pessimistic dry year guess 200'
House:
130' elevation above well head
900' horizontal distance
Very rocky soil
I am looking at using 1-1/4" PVC sch40 or HDPE poly for the in-ground pipe and installing a 1.5HP 7gpm pump. The various calculators tell me that 1200' of pipe would add another ~15' head (plus some for fittings) and the water would travel at 1.8 fps in the pipe.
Adding in the 60psi for the house at high pressure, that would add roughly 140' head for a total of about 485 ft head. That converts to roughly 210 psi at the pump in a dry year:
200' well
130' elevation
15' friction
140' house @ 60psi
---
485' total head
Question 1: If I go to 1" pipe, the friction jumps from 15' to 43' of head. I haven't really added anything for fittings at this point. Does my choice of 1-1/4" seem about right?
Question 2: I would like to use HDPE black poly pipe in the well, since it would be easier to pull by hand. I had a reasonably positive experience pulling a previous poly well and think threading PVC sounds like a chore. However, it seems hard to find HDPE to handle 210 psi + safety margin. Should I just use Sch80 PVC in the well instead? Can anyone comment on handling thick-wall black poly?
Question 3: For the in-ground part, I don't mind gluing PVC but, with rocky soil, I am not sure if I should also use poly for that. Since the pressure is less from the well head upward, I think I can use 160psi or 200psi poly. We are in a seismic region and wasn't sure if poly might also handle shifting better than glued PVC? However, straightening hundreds of feet of stiff poly may be just as much work as gluing PVC.
Question 4: I like the idea of a CSV, but I am worried about increasing the back-pressure at the low end of the pipe. I think the pump could take it, but I don't know about putting even more pressure on poly drop-pipe. We are mostly a household of 2 (occasionally 4) and it looks like the CSV shines more in higher-demand situations. Thoughts?
Thanks again for any feedback. I have found a lot of the older threads here very educational.