I removed old thermostat and only had a 2/22 wire red/white
(I have ran a new 5/22 wire)
Looked at furnace wiring and have 2 black wires from Fan limit switch (one on 24vac transformer other on gas valve terminal)
White wire to thermostat on other gas valve lug, then red wire from thermostat to other terminal of 24vac transformer
I don't see any fan contact wires.
So my question is how do I wire in the new AC condenser and also be able to turn the fan on and off if wanted?

Thank You In Advance
SBAZ
 

Stuff

Well-Known Member
Messages
1,221
Reaction score
130
Points
63
Location
Pennsylvania
With a fan/limit switch the fan has its 120v feed switched. Lots of those old furnaces required an a/c kit to enable fan control. This basically added a relay for the fan in parallel to the fan/limit switch.
 

Stuff

Well-Known Member
Messages
1,221
Reaction score
130
Points
63
Location
Pennsylvania
Picture didn't come through. Do you have a make/model number of the furnace?
 

DonL

Jack of all trades Master of one
Messages
5,205
Reaction score
72
Points
48
Location
Houston, TX
Not really. Do you have a schematic ? That will show what needs to be done. Will also avoid smoking something.

upload_2019-7-25_9-34-38.png





 
Last edited by a moderator:

Stuff

Well-Known Member
Messages
1,221
Reaction score
130
Points
63
Location
Pennsylvania
Something missing here. If there is a condenser then a pro should have been there to install and should be able to wire this. DonL's pic shows old system. Trace from fan/limit switch back to blower to see if there is a relay there.
 

WorthFlorida

Clinical Trail on a Cancer Drug Started 1/31/24. ☹
Messages
5,727
Solutions
1
Reaction score
982
Points
113
Location
Orlando, Florida
Please clear this up. You had a heating forced air furnace and you just had a central air system installed, The A coil was installed above the plenum on this furnace. How did the tech test the AC? Was it agreed that you do the wiring?
 
Top
Hey, wait a minute.

This is awkward, but...

It looks like you're using an ad blocker. We get it, but (1) terrylove.com can't live without ads, and (2) ad blockers can cause issues with videos and comments. If you'd like to support the site, please allow ads.

If any particular ad is your REASON for blocking ads, please let us know. We might be able to do something about it. Thanks.
I've Disabled AdBlock    No Thanks