Is there a diagram out there like with pipe sizing? for both vent and waste.
My sewer line is 4" but I'll be running 3" for toilets and hopefully
3" out the roof, for same setup, one bath above another bath.
Thanks.
 

Sylvan

Still learning
Messages
2,756
Reaction score
689
Points
113
Location
New York
Considering your in NJ the VTR I would use 4" to make sure you don't have hoarfrost problems
 

Terry

The Plumbing Wizard
Staff member
Messages
29,942
Reaction score
3,458
Points
113
Location
Bothell, Washington
Website
terrylove.com
dwv_b1.jpg


An example of a two bathroom stack using wet venting.
 