Most home inspector knew very little on electrical requirements and only a licensed electrical inspector from your local jurisdiction can approve this. Any upgrade would be concernedly cautious. Need a picture of the main panel and all breakers including this one. The location is questionable.
What size wire is it from main panel?
What are you adding that you need more breakers?
What size service at the main panel?
Do you know if it was a licensed electrician who installed this subpanel. There is a sticker on the door. Is it a company logo advertisement?
1. Wire is a 6/3 now for 60a but I have 2-2-2-4 AL ran ready to replace
2. Mini Split AC Unit and another 12/2 up the attic to replace my central air with future heat pump (heat wire). And for future.
3. Service is 200 amp with a 60 amp breaker to subpanel. Replacing 60a with 100a breaker.
Have a Square D QO 24 space 125amp ready to put in. It's not really a whole lot bigger but a few inches each side.
No idea who installed the panel as no marking on the panel. Electrician and inspector I talked to both said they are not sure if that classifies with this.
Exception: In existing dwelling units, service equipment or panelboards that do not exceed 200 amperes shall be permitted in spaces where the headroom is less than 2.0 m (6 and 1/2 feet)
This was part of an addition put on the house in 1991 (subpanel).