Uniform Plumbing Code and AAVs

Users who are viewing this thread

IPDQKWID

Member
Messages
38
Reaction score
3
Points
8
Location
Minnesota
Help. Having looked over the plumbing codes for Minnesota, I think they follow the UPC. The code is published in chapters, with sections such as 310, 702, 910, etc. Where in the world do I find references to AAVs? I don't want to ask the inspector yet, as I don't trust him. He has something against homeowners doing their own remodel.
And maybe an unrelated question, but if the max CFUs on a vent pipe was 24, and you counted 19-20 as the final outcome on your project, would you professionals do a 3" vent out the roof, or be good with a 2" vent? Thank you.
 

Terry

The Plumbing Wizard
Staff member
Messages
29,946
Reaction score
3,460
Points
113
Location
Bothell, Washington
Website
terrylove.com
Venting needs the same area as the waste.
If you have 3" going out, then either a single 3" or we also do two 2" and one 1.5" which combines to make up the same area as a 3".
I would ask the inspector about using an AAV first. Most are okay with it. You need at least one vent through the roof though.
 

IPDQKWID

Member
Messages
38
Reaction score
3
Points
8
Location
Minnesota
Thank you for the replies. At least I can trust the answers here. I have another question regarding venting, and other answers I find online are all over the place. Does the main stack need to be straight? Comes up out of the cement slab on the first level, toilet comes into it on the second floor, at this point it will be difficult to keep the stack straight all the way out the roof. Is that a code thing? I may have to jog the vent stack over a few inches to avoid moving the ceiling joist upstairs.
It seems I'm building the plumbing around the addition, instead of building the addition around the plumbing.
Thank you/
 

Reach4

Well-Known Member
Messages
38,795
Reaction score
4,413
Points
113
Location
IL
Thank you for the replies. At least I can trust the answers here. I have another question regarding venting, and other answers I find online are all over the place. Does the main stack need to be straight? Comes up out of the cement slab on the first level, toilet comes into it on the second floor, at this point it will be difficult to keep the stack straight all the way out the roof.
No.

1. 45 degrees or more from level is considered vertical.
2. Drains can be horizontal, as long as they are tipped downhill a minimum of 1/4 inch per ft. The same for vents above 6 inches above the flood level.
3. When drains are transitioning from vertical to horizontal, 45s or a long sweep must be used. That would usually be the same for horizontal to horizontal. Going from horizontal to vertical can use shorter bends, because clogs seldom happen there.
4. For vents, they must be vertical in the interval below 6 inches below the flood level of any fixtures that vent serves. The flood level is where water would spill onto the floor if the drain clogged.
5. You must go no more than 135 degrees of bends for non-vertical drains without a cleanout.

I may have gotten something off, and I know there is more to it. I am not a plumber.
 

hj

Master Plumber
Messages
33,600
Reaction score
1,037
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
quote; they must be vertical in the interval below 6 inches below the flood level of any fixtures that vent serves.
That should be 6" ABOVE the flood level. And the second requirement is usually ALSO at least 42" above the floor, whichever is HIGHEST.
 

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,771
Reaction score
1,191
Points
113
Location
New England
Your vent line could accumulate condensation or receive precipitation from above...it needs to be able to drain and remain open. Often, in colder climates, the section that actually penetrates the roof (and a ways beneath it)may need to be upsized to prevent hoar frost from closing it off on really cold days. You can get a lot of steam trying to escape when say doing laundry, dishes, a long shower, etc. If it's cold enough, the thing could frost shut.
 

Reach4

Well-Known Member
Messages
38,795
Reaction score
4,413
Points
113
Location
IL
https://www.revisor.mn.gov/rules/?id=4714.0905&format=pdf
UPC section 905.3 is amended to read as follows: 905.3 Vent Pipe Rise. Except as provided elsewhere in this code, each vent shall rise vertically to a point not less than 6 inches (152 mm) above the flood-level rim of the fixture served before offsetting horizontally, and where two or more vent pipes converge, each such vent pipe shall rise to a point not less than 6 inches (152 mm) in height above the flood-level rim of the plumbing fixture it serves before being connected to any other vent.​
 