Looking for opinions (and support of them) for push in wire connectors vs. wire nuts. I know wire nuts when used properly can last for decades, but what about push-in connectors such as the Ideal In-Sure ones?
 

Kreemoweet

In the Trades
Messages
754
Reaction score
66
Points
28
Location
Seattle. WA
They've been around for well over a decade, and I've encountered no failure reports (not that I seek them out, of course).
They're more compact and sometimes much easier to install in a crowded box than wirenuts. Wires can sometimes
pull out as you shove the things into the back of the box, if the wires are both tensioned and rotated in doing so. I wouldn't
dream of using them with (untinned) stranded wire, even though I see some of them are rated for it.
If they're good enough for the Underwriter's Laboratory, and similar listing agencies, they're good enough for me.
 

Bwh

New Member
Messages
7
Reaction score
1
Points
1
Location
Ohio
Agree with kreemoweet - haven't heard any horror stories.

For my money, and time, I'd rather have a good solid twist and wire nut connection. Stab ins can come loose over time, and if you dont push them in all the way, it can exacerbate this issue. Makes a me a little uneasy, so for my money/time I'd go with the "old fashioned" way. You're totally fine using the ideal UL listed push conns.
 

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,770
Reaction score
1,190
Points
113
Location
New England
The hassle with a spring to make the connection is that if it goes through numerous heating/cooling cycles, the tension can begin to relax. If sized properly, they should be fine. I'm not sure they have the fault margin of a proper wire nut, though.
 

WorthFlorida

Clinical Trail on a Cancer Drug Started 1/31/24. ☹
Messages
5,754
Solutions
1
Reaction score
993
Points
113
Location
Orlando, Florida
At the church I maintain I had one of these where the electrician's helper daisy chained too many CFL fixtures (16 or 18 ga wire from the fixture) and one of them actually melted that opened the neutral for about four 42 watt lamp fixtures in a ceiling 23 feet high. The fix was a little wiring change with a wire nut or two done by an electrician.

When wires are twisted together the connection is wire to wire and the wire nut holds the connection together, not necessarily carry current. With the "In-Sure" connection you're going from wire to a connection and the next connection is via a metal tab to another connection that carries the current, etc. Get the picture?

I think these are good if it is making a connection to one fixture or outlet. If you're looking for a butt splice to help with short wires their "SpliceLine" product looks better.
 