    vanity clearance

    Im adding a bath vanity in an existing corner, I plan to build a 4 ft high wall on the other side out 36 " from wall , should I leave enough clearence to clear the vanity top (31") and fill in the 1/2 " on each side of vanity with wood strip or should I leave only room for vanity 30" and saw off...
  2. Jetlag

    Updating Bathroom Circuits to 20 amp

    people run the multiwire brance circuit to kitchen counter GFCI all the time , with half the recepts on each hot leg . Only 2 GFCI s are used with the others fed from the load sides. There is not enough induction to trip the GFCI .
  3. Jetlag

    Updating Bathroom Circuits to 20 amp

    You can share the neutral that way , its called a multiwire branch circuit 2008 NEC 210.4 . You have to be be sure you use a 220/240 double breaker, you can not use a piggy back breaker in which 2 breakers are made together to go on a single lug. If you use that , it will over load the neutral...
  4. Jetlag

    Newbie electrical switching question

    He wont care then . he wants it to stay on after the christmas lights are down , he will just leave the switch on , he will only turn off while the lights are up so not run continuous.
  5. Jetlag

    Newbie electrical switching question

    Am I missing something , If you install a jumper between the hot in and hot out on a timer it is the same as if the timer is not even there , the fact that a switch is in the jumper , returns it to as if the jumper is not there when the switch is off . Unless it is an electronic timer the...
  6. Jetlag

    Grounding I beams on doublewide

    I forgot to say they used a GFCI receptacle in the pump house and protected the light with the GFCI feed out terminals . As far the power co neutral it is grounded at the meter or disconnect to the ground rod . Same as the panel at pump house .
  7. Jetlag

    Grounding I beams on doublewide

    I never said I would do it but connected that way the bare ground becomes the grounded conductor back to the house panel . As far as it not being insulated their argument was the power co wraps their hots around the bare messenger wire which is grounded current carrying conductor .
  8. Jetlag

    Need advice on wiring sump pump outlet for emergency generator / 220v split to(2)120v

    You can use one of the hots on the cable you have for one GFCI and only connect to one hot neutral and ground in the inlet . I just didnt figure you would want to waste the other hot on the 220 . why dont you run another recep from the inlet box somewhere else and connect it to the other hot ...
  9. Jetlag

    Grounding I beams on doublewide

    If you have the power coming in to a lighting outlet , you can no longer run a 14/2 or 12/2 switch leg down to the switch , you must run 12/3 or 14/3 and leave an unused neutral in the switch box . I know what you mean on the pump houses 10/2 w/g was all all people used to use . I ve seen...
  10. Jetlag

    Newbie electrical switching question

    Oh I forgot , if the wirng is 20 amp , #12 wire and it probaby is , you would have to use a 120 volt 20 amp heavy duty switch , not a common 15 amp . You can dertermine the circuit by seeing if the breaker is 15 or 20 amp
  11. Jetlag

    Newbie electrical switching question

    A lot of timers have an on position that overides the timer . You could look into changing it out . Or if you can get another cable the same size as the others (#14 or #12 ) into the timer . If you are lucky the screws on the timer are made to put a wire on both sides and you can add one of the...
  12. Jetlag

    220v to 110v

    Wont scream on that one but he must use a 240 volt 20 amp double breaker in the panel to feed the shared neutral multiwire branch circuit . Even though he will be connecting 2 - 120 v circuits . Set a j box in the closet to tie in the 2 #12 cables to hot tub cable , But you must leave the j...
  13. Jetlag

    Grounding I beams on doublewide

    Here is one for you to chew on , in 2011 code every switch box in a house must contain a neutral wire , no matter if it is needed or not . Reason , so if a DIY needs a neutral for some thing later, he wont tie into the bare ground and use it for a neutral .
  14. Jetlag

    Need advice on wiring sump pump outlet for emergency generator / 220v split to(2)120v

    Only the lucky ones that could afford keroseen in Hoover days
  15. Jetlag

    Need advice on wiring sump pump outlet for emergency generator / 220v split to(2)120v

    Doesnt matter if lights and frig are there , all receptacle outlets in unfinished basement , garage , or crawl space must be GFCI . Does not matter if it is wet or damp , it can be dry as a bone . Some of the parents didnt survive , because of electrocution . If the gfci has saved poeple , it...