Recent content by davie

  1. davie

    Advice on Fine-Tuning Primary/Secondary Pumps

    Thanks again for your advice. I think the easy answer is no. Your point about the total boiler running time is well noted.
  2. davie

    Advice on Fine-Tuning Primary/Secondary Pumps

    I forgot to put directional arrows on the drawing.
  3. davie

    Advice on Fine-Tuning Primary/Secondary Pumps

    It's not that the zones don't match. The temperature difference I'm fretting about (maybe unnecessarily) is across the hydraulic separation —i.e. closely spaced tees— between boiler pump and zone pump. From my observations it seems a good portion of the hot water supply coming from the boiler...
  4. davie

    Advice on Fine-Tuning Primary/Secondary Pumps

    That makes complete sense. Looks like an autocorrect error here, but I can't make sense of it.
  5. davie

    Advice on Fine-Tuning Primary/Secondary Pumps

    What will measuring the amperage tell me?
  6. davie

    Advice on Fine-Tuning Primary/Secondary Pumps

    If I separated the rads from the floors, what would you then change? Send hotter water to the rads? Just to clarify, when you say "loop," do you mean in series? The emitters are all in parallel within the zones.
  7. davie

    Advice on Fine-Tuning Primary/Secondary Pumps

    I agree that if the cool return water from the zones heading to the boiler is crucial. In the image above, the cool water returning from the zones is at 84F. The problem that I see is that the water returning to the boiler is hotter 88F. More to the pount, I'm not happy with the 9F split between...
  8. davie

    Advice on Fine-Tuning Primary/Secondary Pumps

    The boiler isn't short cycling (currently 15-45 cycles per day). Any thoughts as to how I can get a slower flow rate, if that's what you're saying I need? What mode would you use on the Taco VT2218?
  9. davie

    Advice on Fine-Tuning Primary/Secondary Pumps

    Could changing the primary and secondary pump flow rates be a way to get more heat out to the zones? I'm confused as to why there always seems to be a temperature drop between the primary supply and the secondary supply. There often seems to be a ~10F drop between the supply from the boiler and...
  10. davie

    Advice on Fine-Tuning Primary/Secondary Pumps

    The piping is under 7/8" tongue and groove subfloor and 3/8" hardwood.
  11. davie

    Advice on Fine-Tuning Primary/Secondary Pumps

    60C (140F) is what's required to heat my house at -17C (1F), based on the heat loss for my house, and the emitters we installed. In the past winter, we only had a few days that got close to that temperature, around 5F (-15C), but the house was cozy on those days. Actually, more cozy than usual...
  12. davie

    Advice on Fine-Tuning Primary/Secondary Pumps

    It's hardwood flooring (3/8") with tongue and groove subfloor (7/8"). (NB: the actual insulation used is R22, and I didn't use a reflective foil.) I don't have a floor sensor, but I designed the system maximum temperature with this in mind. At design temperature, with the effective R1.85...
  13. davie

    Advice on Fine-Tuning Primary/Secondary Pumps

    That's right, it's all one temperature. Design system temperature is 140F (at 1F outdoor temp), and max temp is 154F. Minimum system temperature is 93F.
  14. davie

    Advice on Fine-Tuning Primary/Secondary Pumps

    The delta t in the primary loop is comparable to the secondary, when temperatures are higher. Yesterday the delta t was 9F in the primary and 9F in the secondary. When the weather gets colder, the primary delta t will increase. I have data from a day in March, for instance, the outdoor...
  15. davie

    Advice on Fine-Tuning Primary/Secondary Pumps

    A few years ago, I got some great help here doing heat loss calculations, choosing a boiler, and designing a radiant system for my home. The system is installed now, and it ran well all last winter. I'm very happy with how efficient it has been, and how comfortable it is. Thanks to everyone who...
Top
Hey, wait a minute.

This is awkward, but...

It looks like you're using an ad blocker. We get it, but (1) terrylove.com can't live without ads, and (2) ad blockers can cause issues with videos and comments. If you'd like to support the site, please allow ads.

If any particular ad is your REASON for blocking ads, please let us know. We might be able to do something about it. Thanks.
I've Disabled AdBlock    No Thanks