Recent content by Cuzzinred

  1. Cuzzinred

    ECM 3.0 motor ?

    This unit's delay times are programmed into the module on the blower motor. Replaced with an original type, everything back to normal. Thanks for the information and help.
  2. Cuzzinred

    ECM 3.0 motor ?

    Yes, both come on at the same time. I believe I’ve got it figured out, will know for sure tomorrow!
  3. Cuzzinred

    ECM 3.0 motor ?

    Correct !
  4. Cuzzinred

    Gas fireplace options - advice

    What you have is stand alone firebox, you can put a set of gas logs inside the box. Unvented logs are the way to go, you’ll need to close the damper in the chimney so you want be sending heat out. Unvented logs and heaters utilize an ODS pilot, which means if the oxygen level get unsafe in...
  5. Cuzzinred

    Water Heater Pilot Won't Stay Lit

    Is your pilot a stable blue flame or does it have a yellow tip ? If it nice and blue, is the flame surrounding the top 1/3 or so of the tip of thermocouple ? If it’s yellow tips, the pilot itself will need cleaning. LP gas or Natural?
  6. Cuzzinred

    ECM 3.0 motor ?

    I can’t say if it ever worked properly, blower stopped working so I replaced it and noticed it wasn’t any delay. I’ve swapped blower with a know good one and replaced the control board, same results. I’m thinking about adding the missing R wire, do you see any problems with that ?
  7. Cuzzinred

    White-Rodgers gas valve leaking vent

    Probably going to need a new valve, sounds if debris got into the valve and not letting It seat properly. I have seen this clear itself after a few cycles, but very rarely!
  8. Cuzzinred

    ECM 3.0 motor ?

    A I’ll have to recheck but I believe it was at transformer itself. Motor name plate as in indoor Blower motor ? I’ll try and get it for you. Seems like it was a genteq motor also
  9. Cuzzinred

    ECM 3.0 motor ?

    It’s a standard mercury bulb T-stat,
  10. Cuzzinred

    ECM 3.0 motor ?

  11. Cuzzinred

    ECM 3.0 motor ?

    Jumped across R-W , works just the same. What I have notice is my wiring diagram on the unit doesn’t have a red wire coming from contactor to the Heat ACB terminal on control board like the wiring diagram shown in the install manual above.!
  12. Cuzzinred

    ECM 3.0 motor ?

    Back to the drawing board lol I installed new control board, same problem !
  13. Cuzzinred

    ECM 3.0 motor ?

    Thank you for the info ! I’ve looked high and low for an operational manual, I tested the control board for 24 vac going to the x13 fan (first one I’ve had experience with by the way ) I lost 24 vac as soon as t-stat satisfied. My original thinking was that maybe the module in the x13 held the...
  14. Cuzzinred

    ECM 3.0 motor ?

    Air Ease / M’fed by Allied Air Enterprise M# RPGE13A36100-3A
  15. Cuzzinred

    ECM 3.0 motor ?

    On these motors, Do they have delay times programmed into them or does the control board on the unit (gas pack)handle the delay times ? Mine is stopping as soon as the t-stat is satisfied, no delay to purge the heat out of the chamber.