If I turn the Wye up like this on the WC is it still a properly vented bathroom group if my vent is off of the lav?
 

Omolo

New Member
Messages
14
Reaction score
0
Points
1
Location
Ohio
If I turn the Wye up like this on the WC is it still a properly vented bathroom group if my vent is off of the lav?

567CFB0A-B9C4-4774-9EA7-9190185F55AE.png
 

wwhitney

In the Trades
Messages
6,563
Reaction score
1,844
Points
113
Location
Berkeley, CA
Yes, for the IPC, no for the IRC.

Ohio appears not to have adopted the plumbing sections of the IRC that would prohibit that arrangement, and have amended the IPC to apply to dwellings subject to the IRC. So if this is in Ohio, it's OK.

However, I believe some on this forum have argued that it's suboptimal, and you'd be better off moving the drain line out from under the closet flange, and then using a closet bend into a horizontal wye. Which is what the IRC would require.

Cheers, Waye
 

Omolo

New Member
Messages
14
Reaction score
0
Points
1
Location
Ohio
Yes, for the IPC, no for the IRC.

Ohio appears not to have adopted the plumbing sections of the IRC that would prohibit that arrangement, and have amended the IPC to apply to dwellings subject to the IRC. So if this is in Ohio, it's OK.

However, I believe some on this forum have argued that it's suboptimal, and you'd be better off moving the drain line out from under the closet flange, and then using a closet bend into a horizontal wye. Which is what the IRC would require.