Is it legal to use a schedule 40 fitting in a DWV application for a trap primer?

Users who are viewing this thread

Messages
32
Reaction score
10
Points
8
Location
Seattle Area
I need to install a trap primer for a couple of new construction emergency floor drains, and I'm under the UPC. There are a few solutions which go between the drain and trap that allow a 1/2" FPT connection from the trap primer, but they are all very backordered as far as I can tell.

However one of these options would get the job done:
1: https://www.supplyhouse.com/Spears-402-247-2-x-2-x-1-2-PVC-Sch-40-Threaded-Tee-Socket-x-FIPT

2: Glue one of these into a 2x2x1.5" san-tee: https://www.supplyhouse.com/Spears-438-247-2-x-1-2-PVC-Schedule-40-Spigot-x-Female-Bushing

Seems completely functional and equivalent to the commercially available but backordered solution: https://www.siouxchief.com/products...trap-primers/trap-primers/trap-primer-adapter

Do you think an inspector would question either of these alternative solutions?
 

John Gayewski

In the Trades
Messages
4,324
Reaction score
1,319
Points
113
Location
Iowa
Drainage requires recessed drainage pattern fittings. Not to say I've never used sched 40 on drainage, but when you look inside of the pipe you can see why. It leaves huge gaps between the end of the pipes. The sewer solids and water take a turbulent path with lots of lips and edges.

In the right configuration I think most inspectors would accept the bushing in a santee.
 

wwhitney

In the Trades
Messages
6,532
Reaction score
1,822
Points
113
Location
Berkeley, CA
I happen to have one of those on hand, so if you want to see what John is referring to, there's a picture below. The ID of the hubs is ~2.38" (for the 2.375" OD of 2" Schedule 40 pipe), and the ID of the ~1" between the two hubs is ~2.30". Versus the ID of a Schedule 40 DWV PVC pipe, which is ~2.0".

Cheers, Wayne
 

Attachments

  • PXL_20220614_020509426.jpg
    PXL_20220614_020509426.jpg
    81.9 KB · Views: 124

Reach4

Well-Known Member
Messages
38,795
Reaction score
4,413
Points
113
Location
IL
AFAIK, UPC does not allow PVC pressure piping indoors. I don't know if that applies to pipes and fittings in the slab.
 

Jeff H Young

In the Trades
Messages
8,753
Reaction score
2,164
Points
113
Location
92346
I suppose a santee with bushing might be ok like a 2" x 1/2 inch fip bushing how about a tapped castiron trap? I never seen an abs trap tapped for primer. or tapped drain body? but i only used cast iron traps those should be easy to find
 

John Gayewski

In the Trades
Messages
4,324
Reaction score
1,319
Points
113
Location
Iowa
I suppose a santee with bushing might be ok like a 2" x 1/2 inch fip bushing how about a tapped castiron trap? I never seen an abs trap tapped for primer. or tapped drain body? but i only used cast iron traps those should be easy to find
The souix cheif finish line floor drains come with an inlet for trap primer they are plastic.
 

Jeff H Young

In the Trades
Messages
8,753
Reaction score
2,164
Points
113
Location
92346
I meant plastic p traps being tapped but good to know the drains are tapped
 