Forgive me if this is the wrong place to ask this..... I am replacing a standby generator with a larger one. Basically disconnecting it from the current gas line (2psi regulated down) and reconnecting to the larger one. I know I need to pull a permit to do this, but what will the inspection need ? Will the entire gas line inside the house need to be checked again ? And would that entail capping everything and represurizing it for the inspector ?
 

Fitter30

Well-Known Member
Messages
4,292
Reaction score
778
Points
113
Location
Peace valley missouri
If theres a valve where line is teed off and one before the generator and a tee with a pressure tap between the two valve. After pressuring closing both valve with gauge installed should check line.
 

John Gayewski

In the Trades
Messages
4,325
Reaction score
1,319
Points
113
Location
Iowa
This is a question for the inspector. Ask him what he wants to see. Fill him in on what your doing.
 

Breplum

Licensed plumbing contractor
Messages
1,904
Reaction score
767
Points
113
Location
San Francisco Bay Area
If the primary line is not changed, then just replacing equipment and a few feet of pipe is not pressure tested.
A leak test via squirt/soapy water, leak test solution or gas sniffer is likely all that would be called for by an inspector.
And, you won't know unless you ask.
 

RonL1

Member
Messages
46
Reaction score
3
Points
8
Location
Fort mill, sc
If the primary line is not changed, then just replacing equipment and a few feet of pipe is not pressure tested.
A leak test via squirt/soapy water, leak test solution or gas sniffer is likely all that would be called for by an inspector.
And, you won't know unless you ask.
Have to figure out who that would be... guess Acala to the permit office is in order.....