Hello, which 4" drain pipe would last longest and without issues? I see a lot of foam core with a thin wall, it doesn't seem good. I'm guessing running a snake down a foam core can damage the thin wall.

ABS doesn't flex much? And if there's seismic movement, the fittings can fail?

ABS temp range is 40-170
PVC temp range is 33-140
 

WorthFlorida

Clinical Trail on a Cancer Drug Started 1/31/24. ☹
Messages
5,727
Solutions
1
Reaction score
982
Points
113
Location
Orlando, Florida
Since you're in seismic territory check your local jurisdiction. Supporting the pipe and bracing can be part of the local codes. FYI, all drain pipe is schedule 40 minimum. It's not thin wall.
 

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,770
Reaction score
1,190
Points
113
Location
New England
While I agree, CI is the premium product, the choice of plastic often depends on what you can get locally and, it's not a good idea to mix them in the same system. Some applications don't recommend foam core pipe, but it is cheaper if it works for that application. With CI, you don't see as much leaded hubs as it takes more skill, hubless stuff works well, too.

There are industry guidelines on how to lay out the plastic piping. The plastics require a bit more planning especially if you have longer runs, as they change length MUCH more than CI piping does. Too much expansion/contraction can put huge stresses on the pipe, and can cause it to literally tear itself, and often make some noises...it's hard on the fittings, too. Expansion fittings to accommodate length changes tend to also be expensive if needed.
 

John Gayewski

In the Trades
Messages
4,324
Reaction score
1,319
Points
113
Location
Iowa
PVC is better drain pipe than cast iron. The smoothness alone makes it a better choice it also last longer than cast. Between abs and pvc I'd choose pvc because that's what's available here and that's what i am used to working with. People quit using abs here in the 80's. I've twisted abs fitting off of pipe with my bare hands.
 

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,770
Reaction score
1,190
Points
113
Location
New England
Quiet operation and fire codes can dictate CI is better and required in some situations. While PVC is self-extinguishing, in a multi-story dwelling, a fire in one unit could make all of the floors above uninhabitable if the pipe was damaged. That rarely would happen with CI. There's a place. The CI pipe in the house I grew up in is still in fine shape as I found when I needed to do some modifications during a remodel. That's like 70-years now.
 

John Gayewski

In the Trades
Messages
4,324
Reaction score
1,319
Points
113
Location
Iowa
The cast iron in some of our buildings is around 100 years old. It clogs. The fire thing, is what it is. That doesn't make it better drainage pipe. It makes it fireproof not better for drainage. Sound should be mitigated. If you don't mitigate the sound cast iron pipe is still noisy. So since we're mitigating let's use the better pipe for the job. Selecting a pipe for a secondary purpose doesn't make the first choice worse, just not applicable in that specific instance. Most times you only need cast iron on fire walls or in plenums. In those instances we're try to use sections of cast iron.

I've since many projects in cast iron and don't have a problem with it. I actually like running it. It's just not better drainage pipe.
 

Mr tee

In the Trades
Messages
354
Reaction score
145
Points
43
Location
Montana
Use whichever plastic is more available in your area, probably ABS. Cast iron is much more expensive and requires tools you may well never use again. If you need to meet fire code, such as through the wall into a garage, a couple shielded bands and one cast iron fitting is normally all that is necessary.
 

Sylvan

Still learning
Messages
2,756
Reaction score
689
Points
113
Location
New York
While I agree, CI is the premium product, the choice of plastic often depends on what you can get locally and, it's not a good idea to mix them in the same system. Some applications don't recommend foam core pipe, but it is cheaper if it works for that application. With CI, you don't see as much leaded hubs as it takes more skill, hubless stuff works well, too.

There are industry guidelines on how to lay out the plastic piping. The plastics require a bit more planning especially if you have longer runs, as they change length MUCH more than CI piping does. Too much expansion/contraction can put huge stresses on the pipe, and can cause it to literally tear itself, and often make some noises...it's hard on the fittings, too. Expansion fittings to accommodate length changes tend to also be expensive if needed.


"it's not a good idea to mix them in the same system"

Many times I have used PVC for venting and connection to the NHCI with no hub couplings

Knowing sewer and drain fumes can corrode CI and other ferrous metals then plastic is a better choice for venting especially true when some areas now ban the use of a building house trap

PVC does not have as much of a bearing load as CI so under ground use is limited on applications

PVC should never be exposed to direct sun light

As I stated before CI is the QUIET pipe besides offering decades of trouble free service

Over 90% of my roof drains were installed using a caulked joint and 3' x 3'
x 4 PSF sheet lead.

I still like to use XHCI caulked joints under ground as the
systems I work on are over 100 years old so CI has proven long term trouble free systems

If a CI system is properly and the ground soil conditions are not acidic and cinders for example are not used in the CLEAN BACK FILL then one can expect decades of trouble free drainage

The reason some people push PVC is their skill level maybe
compromised such as lead wiping which we still do on occasions some other may have no clue how to even prepare a joint or do a lead burned joint

PVC requires a saw, primmer and glue and anyone can install it

I love driving and while upstate NY I noticed some children installing underground drainage and spoke to the adult farmer standing by then

He said his 7 year old daughter plumbed the house along with his 9 year old son .

They did an outstanding job NO wet venting or cheater venting as they were working on a new home on his property as a small guest house

 

Sylvan

Still learning
Messages
2,756
Reaction score
689
Points
113
Location
New York
Use whichever plastic is more available in your area, probably ABS. Cast iron is much more expensive and requires tools you may well never use again. If you need to meet fire code, such as through the wall into a garage, a couple shielded bands and one cast iron fitting is normally all that is necessary.[/QUOTE

Your right it is for CHEAP installations when people don't mind a system that is proven to be dangerous to the installers and inhalants


https://saferchemicals.org/get-the-facts/toxic-chemicals/vinyl-chloride/
 

Sylvan

Still learning
Messages
2,756
Reaction score
689
Points
113
Location
New York
Hello, which 4" drain pipe would last longest and without issues? I see a lot of foam core with a thin wall, it doesn't seem good. I'm guessing running a snake down a foam core can damage the thin wall.

ABS doesn't flex much? And if there's seismic movement, the fittings can fail?

ABS temp range is 40-170
PVC temp range is 33-140


Actually water temperature of 150 DEF or above is not allowed down a drainage system for several reasons

1- It can scald workers in the sewer

2- In the winter the non tempered water can crack the sewer piping

803.1 Wastewater temperature.

Steam pipes shall not connect to any part of a drainage or plumbing system and water above 150°F (66°C) shall not be discharged into any part of a drainage system. Such pipes shall discharge into an indirect waste receptor connected to the drainage system.
 

Jeff H Young

In the Trades
Messages
8,754
Reaction score
2,164
Points
113
Location
92346
CA ABS far more common however recent years 10 years or so I see some PVC . When outside building by a few feet it gets called sewer and allows thinner pipe. generally inside building ABS sch 40 is used more , I can't really say why just been that way since my first day on the job I've installed very little PVC within building
 

Holeshot

New Member
Messages
16
Reaction score
1
Points
3
Location
California
I'm replacing a 40 year old under-slab cast iron pipe in a residential single story that's in pretty bad condition. The soil has a lot of clay. The original CI has a lot of back filled sand.

Ferguson and other wholesalers only sells ABS foam core, no ABS solid core.
The ABS schedule 40 foam core: Has 3 layers. Inner and outer solid core skins with foam core in the middle.
Minimum solid core skin thickness: .015", 15 thousandths of an inch. That's roughly 1/2 the thickness of a credit card.
4" ABS total wall thickness: 0.237"

The SoFi Stadium development in Los Angeles used large diameter PVC pipe for sewer lines in the public street. I wonder why they didn't use ABS?

In Los Angeles, what's available is ABS foam core schedule 40, PVC schedule 40 and CPVC schedule 80

CPVC schedule 80
4" x 20' = $379.57
4", 45 degree elbow = $57.89
Max temp 200F
Min temp 33F
Tensile strength 8200 PSI

PVC schedule 40
20' x 4" = $166.95
Max temp 140F
Min temp 33F
Tensile strength 7500 PSI

ABS schedule 40
20' x 4" = $107.38
Tensile strength 4500 PSI
Max temp 140F
Min temp 32F
 

Sylvan

Still learning
Messages
2,756
Reaction score
689
Points
113
Location
New York
I'm replacing a 40 year old under-slab cast iron pipe in a residential single story that's in pretty bad condition. The soil has a lot of clay. The original CI has a lot of back filled sand.

Ferguson and other wholesalers only sells ABS foam core, no ABS solid core.
The ABS schedule 40 foam core: Has 3 layers. Inner and outer solid core skins with foam core in the middle.
Minimum solid core skin thickness: .015", 15 thousandths of an inch. That's roughly 1/2 the thickness of a credit card.
4" ABS total wall thickness: 0.237"

The SoFi Stadium development in Los Angeles used large diameter PVC pipe for sewer lines in the public street. I wonder why they didn't use ABS?

In Los Angeles, what's available is ABS foam core schedule 40, PVC schedule 40 and CPVC schedule 80

CPVC schedule 80
4" x 20' = $379.57
4", 45 degree elbow = $57.89
Max temp 200F
Min temp 33F
Tensile strength 8200 PSI

PVC schedule 40
20' x 4" = $166.95
Max temp 140F
Min temp 33F
Tensile strength 7500 PSI

ABS schedule 40
20' x 4" = $107.38
Tensile strength 4500 PSI
Max temp 140F
Min temp 32F


Is relining an option ???

https://flow-liner.com/


https://curaflo.com/?gclid=CjwKCAiA...UrgHBSQE4KDfJk9aLHo_tPMzupWgTwVBoCzV4QAvD_BwE
 

Reach4

Well-Known Member
Messages
38,796
Reaction score
4,412
Points
113
Location
IL
PVC schedule 40 is available in solid and foamcore. At least some of the solid is triple rated for DWV, pressure, and well casing.
 

Jeff H Young

In the Trades
Messages
8,754
Reaction score
2,164
Points
113
Location
92346
400 a stick for CPVC I think I'd pass. I'd need a reason not to use what I been using since 87 ABS. Not saying its best just what I've used on a few thousand homes
 

Jeff H Young

In the Trades
Messages
8,754
Reaction score
2,164
Points
113
Location
92346
btw never seen ABS on big jobs I've done big jobs In Irvine and Newport PVC sometimes I've used CPVC in lab work. Homes were 99 percent I think its less maybe 90 percent ABS just drove by a 200 plus unit apartments its ABS under slab . What SOFI wouldn't sway me though interesting
 

Holeshot

New Member
Messages
16
Reaction score
1
Points
3
Location
California

There's a section that's sloping pretty bad under the slab. Relining probably wouldn't work in that section. The main line from sidewalk to the house can be relined but I'm not aware of relining the other branches under the slab. I guess the only way is to cut open sections of the slab to reline and connect the transitions? I rather not cut up the slab.

I'm guessing the schedule 80 CPVC would last a lot longer than ABS? Over 300 years?

The underslab PVC sewer lines pic I found off the internet
 

Attachments

  • IMG_20191005_170228.jpg
    IMG_20191005_170228.jpg
    96.5 KB · Views: 129
  • IMG_20191009_144042.jpg
    IMG_20191009_144042.jpg
    84.4 KB · Views: 130
  • IMG_20191030_181249.jpg
    IMG_20191030_181249.jpg
    105.4 KB · Views: 125
  • IMG_20200607_190836.jpg
    IMG_20200607_190836.jpg
    64 KB · Views: 162
  • IMG_20200607_190948_1.jpg
    IMG_20200607_190948_1.jpg
    78.1 KB · Views: 128
  • IMG_20200607_191052_1.jpg
    IMG_20200607_191052_1.jpg
    61.1 KB · Views: 149
  • Sewer-Drains-Under-Slab-768x576.jpg
    Sewer-Drains-Under-Slab-768x576.jpg
    96.4 KB · Views: 183

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,770
Reaction score
1,190
Points
113
Location
New England
If the slope of the under slab stuff is not correct, or you have other problems with it and aren't willing to tear up the slab, you may end up deciding to block that section off and reroute the run outside of the slab. That would still require getting it outside of the building, but might not require tearing up the slab, or if it does, not that much, depending on where the lines run.
 