Where to put cleanouts?

Users who are viewing this thread

Wren

Member
Messages
57
Reaction score
6
Points
8
Location
Athens, GA
I've drawn up my horizontal drain lines and want to get some input as to where I'll need to place the cleanouts. The house was built in 1920 and is on piers with a crawlspace.

I'm thinking about using a 3" combo wye on it's side with cleanout fitting at A in the drawing due to the fact that I'll have to have a quarter turn at that point to connect into the main branch drain. The cleanout will have to be in the crawlspace, which I understand isn't the ideal location, but I don't see that I have much choice.

Due to the layout of the crawlspace and the lack of headroom, it's going to be very difficult to have a cleanout at the full bath WC (left hand side of drawing) and I think the inspector will let me get away without one. My plumbing buddy says that one can always pull the toilet if that line has to be snaked. I don't think that is necessarily exactly to code, but it gets done of course.

At E in the drawing, I had considered using a long sweep quarter turn and then having a wye with a cleanout just upstream of it instead of the two 1/8-turn elbows separated by a length of pipe. Which would be better?

Where else should I put one if it's needed? Basically, the inspector told me that there needs to be a cleanout every time a horizontal line has a quarter turn fitting, although two 1/8-turn fittings separated with some distance of pipe appears to be acceptable.

At D where the 4' vertical drop where the drain goes underground then turns horizontal, do I need a cleanout at the base of the stack where it goes back to horizontal before exiting and connecting to the sewer stub? It's only about 12' between the vertical/horizontal junction and the city's cleanout at the stub. If I do, how should that be configured? A combo fitting with cleanout?

I know there are a lot of considerations here and I'm grateful for any insights.

Thanks!

zIndwAw.jpg
 

Breplum

Licensed plumbing contractor
Messages
1,903
Reaction score
767
Points
113
Location
San Francisco Bay Area
I speed read your words, but quick reply:
"A" yes to a cleanout extended to the exterior.
kitchen sink always needs a cleanout, either combo below the stack or a cleanout/'test' tee in the vertical
no matter at E/C, long sweep is fine and simpler.
All horizontal runs on a main floor greater thatn 5' need a cleanout AND all horizontal change of direction greater than 135 degrees
A two way cleanout at the exterior stub out will serve that final end.
 

Wren

Member
Messages
57
Reaction score
6
Points
8
Location
Athens, GA
Thanks very much for the reply.

"A" yes to a cleanout extended to the exterior.

The only problem with extending the pipe at A to the outside of the house is that it would have to go through a block wall that is about 10' away with limited headroom going towards the back of the house in the crawlspace. In the drawing, the rear of the house is on the bottom. I'll take another look at it when I return tomorrow.

kitchen sink always needs a cleanout, either combo below the stack or a cleanout/'test' tee in the vertical

I've read that a trap adapter can be used instead of a cleanout. Would that be acceptable? The sink will have an AAV as suggested by the inspector due to a large window and the difficulty in putting a regular vent through the roof at that location.

no matter at E/C, long sweep is fine and simpler.

Would the cleanout at A be sufficient to provide a cleanout all the way to E, or do I need to put a wye with cleanout just before the quarter turn?

All horizontal runs on a main floor greater than 5' need a cleanout AND all horizontal change of direction greater than 135 degrees

It sounds like it would be preferable to have a cleanout in the line from the full bath/laundry to where it meets the main branch drain (main branch runs top of drawing to bottom of drawing), but I'm not sure where I could fit one in due to grade and footing restrictions.

A two way cleanout at the exterior stub out will serve that final end.

I'm not certain if the city's stub cleanout is a two way or not. I'll have to look as I've not yet finished digging down to it. Typically in our town, they want you to have a cleanout at the house and at the street, but there's only about 15' from the front door to the street, so the inspector said one would be sufficient.
 
Last edited:

Sylvan

Still learning
Messages
2,756
Reaction score
689
Points
113
Location
New York
Rule of thumb

1- CO every change of direction greater then 45DEG

2- CO installed at the base of every stack

3- CO installed ever 100 feet

4- A toilet can be considered as a CO depending on local codes as it is easily removed and placed back

5- Each fixture trap has a CO plug ( by code) so this is a CO

sylvan-snaking-02.jpg
 

Tuttles Revenge

In the Trades
Messages
4,132
Reaction score
1,410
Points
113
One at each run for bathrooms (end of line CO). One at the laundry that is accessible w/o moving the washer.. typically on the vent without offset to the drain. One on the kitchen sink above the trap arm.. that way you don't have to take the sink apart and can run water down the drain while snaking to flush out crud. Not entirely sure the layout of the one bathroom, so I changed the layout how I would.. but definately just a suggestion based on min info.
Cleanouts.jpg
 

Wren

Member
Messages
57
Reaction score
6
Points
8
Location
Athens, GA
Thanks very much for the reply.


Can the access for the AAV at the washer drain be used as an access point for a clean out by removing the AAV? I'm planning on using one of the AAV boxes that goes in the wall with a cover for servicing it. If that's not acceptable, does one put a cleanout in the vent pipe and then have a hole in the sheetrock for access, or?
 

Tuttles Revenge

In the Trades
Messages
4,132
Reaction score
1,410
Points
113
Thanks very much for the reply.


Can the access for the AAV at the washer drain be used as an access point for a clean out by removing the AAV? I'm planning on using one of the AAV boxes that goes in the wall with a cover for servicing it. If that's not acceptable, does one put a cleanout in the vent pipe and then have a hole in the sheetrock for access, or?

I would think that a removable AAV would be acceptable. Ive never done it as such myself, but it does meet the definition. Sylvan mentions that toilets are acceptable as accessible cleanouts, but not under our code.

Other methods for a stand alone cleanout would be a Cleanout Tee installed so that just the CO plug is protruding from the sheetrock, maybe with a cover, San Tee with CO adapter glued in and that adapter sticking out of the sheet rock, sometimes with a domed cleanout cover. Or a Wye with CO adapter. We normally use a CO Tee for its simplicity.
 

Sylvan

Still learning
Messages
2,756
Reaction score
689
Points
113
Location
New York
Lordy. Now I think I have seen it all. :Do_O:eek:



You would be smiling also knowing your making $450 for snaking the 4" main sewer and removing roots and it took less then a 1/2 hr and this job was 7 minutes from my office not to bad for a 70+ year old

Yesterday and today I hit a gold mine water Jetting CHA CHING
 

Reach4

Well-Known Member
Messages
38,796
Reaction score
4,412
Points
113
Location
IL
Wren, what on your diagram do you expect to leave as is, and what part will be changing?
 

Wren

Member
Messages
57
Reaction score
6
Points
8
Location
Athens, GA
Wren, what on your diagram do you expect to leave as is, and what part will be changing?

I went and crawled around under the house and I think I can add a CO to the half bath that will go to the outside if I cut a hole in the non-structural skirting blocks. It's about 11' from the combo coming off of the WC.

Is it OK to have such a long cleanout pipe?

Also, is it acceptable to have a couple of 22-1/2° bends in the cleanout pipe? There are a couple of piers in the way and that's the only way I can get it outside. Also, can the cleanout coming off of the combo fitting from the WC be a 2" pipe instead of a 3"? 2" would mean a smaller hole to drill in the skirting blocks.

Here's what I believe will work:

ZgeDjvJ.jpg



And a mock up with all 3" pipe, although I would like to use 2" for the CO branch (pipe lengths are not to scale). Can 2" be used instead of 3"?

1kfNjn3.jpg




Also, I'm looking at adding a CO to the full bath that will exit to the side of the WC as shown in Tuttle's Revenge's post but I need to look at how that would affect my french drain, etc. The full bath WC is on an outside wall.


You would be smiling also knowing your making $450 for snaking the 4" main sewer and removing roots and it took less then a 1/2 hr and this job was 7 minutes from my office not to bad for a 70+ year old

Yesterday and today I hit a gold mine water Jetting CHA CHING

$900/hr. ain't too bad no matter your age or where you are!
 
Last edited:

Sylvan

Still learning
Messages
2,756
Reaction score
689
Points
113
Location
New York
You need to have a full size pipe, so a full size cutter blades can be run


Full size YES up to 4"

4" can be used up to 8" or more

IPC - 708.7 Minimum size.
Cleanouts shall be the same nominal size as the pipe they serve up to 4 inches (102 mm). For pipes larger than 4 inches (102 mm) nominal size, the size of the cleanout shall be not less than 4 inches (102 mm).

Exceptions:

1. "P” trap connections with slip joints or ground joint connections, or stack cleanouts that are not more than one pipe diameter smaller than the drain served, shall be permitted.

2. Cast-iron cleanout sizing shall be in accordance with referenced standards in Table 702.4, ASTM A 74 for hub and spigot fittings or ASTM A 888 or CISPI 301 for hubless fittings.

IPC - 708.8 Clearances.

Cleanouts on 6-inch (153 mm) and smaller pipes shall be provided with a clearance of not less than 18 inches (457 mm) for rodding. Cleanouts on 8-inch (203 mm) and larger pipes shall be provided with a clearance of not less than 36 inches (914 mm) for rodding.
 

Wren

Member
Messages
57
Reaction score
6
Points
8
Location
Athens, GA
3" it is.

I assume that it's acceptable to put in a couple of 1/16-turn elbows in the CO branch before it gets to the combo coming from the half bath, correct?

Also, is it possible to get a cleanout adapter that fits down inside of a pipe or do they all go on the outside of the pipe?
 
Last edited:

Jeff H Young

In the Trades
Messages
8,759
Reaction score
2,166
Points
113
Location
92346
never heard of clean outs not being required due to having a toilet to remove. using the AAV for a clean out would work relatively easy but I wouldn't argue it with an inspector and would expect a correction notice
 