According to the Canadian building code:
9.23.5.3. wall studs

(1) wall studs shall not be notched, drilled or otherwise damaged so that the undamaged portion of the stud is less than two-thirds the depth of the stud if the stud is loadbearing or 40 mm if the stud is non-loadbearing, unless the weakened studs are suitably reinforced.

How do you run a 1.5" ABS pipe through a single 2x6 stud then? One third of a 2x6 is slightly less than 1 7/8" which isn't big enough to run the ABS pipe. I see that Simpson makes stud shoes, but those don't seem to be available anywhere and even then, seem to require engineering sign off rather than being a sure fix.

Other places say that you can double up the stud as long as you aren't drilling more than two consecutive pairs, but that seems to be in the US vs Canada.
 

Reach4

Well-Known Member
Messages
38,880
Reaction score
4,433
Points
113
Location
IL
How do you run a 1.5" ABS pipe through a single 2x6 stud then? One third of a 2x6 is slightly less than 1 7/8" which isn't big enough to run the ABS pipe.
1.5 inch copper is 1.625 od.

Are you sure the studs are load bearing?
 

Tee Jay

New Member
Messages
28
Reaction score
0
Points
1
Location
Edmonton
Are you sure the studs are load bearing?

Yes, 100% certain it is load bearing. I'd have to go on a hunt for copper that size, the local hardware stores can't even get 1/2 and 3/4 these days. Would certainly prefer to stay with ABS.
 

Reach4

Well-Known Member
Messages
38,880
Reaction score
4,433
Points
113
Location
IL
Yes, 100% certain it is load bearing. I'd have to go on a hunt for copper that size, the local hardware stores can't even get 1/2 and 3/4 these days. Would certainly prefer to stay with ABS.
1-1/4 inch ABS is 1.660 OD. That probably works for a lavatory, but not a kitchen.
 

wwhitney

In the Trades
Messages
6,563
Reaction score
1,844
Points
113
Location
Berkeley, CA
For a 5.5" member with an allowable hole size of 1.83", if you drill a 2.13" hole and use a Simpson HSS2-SDS1.5 stud shoe to reinforce it (which would require not centering the hole), unless your inspector is unreasonably picky, that would count as "suitably reinforced."

If you're concerned, ask your building department how they interpret "suitably reinforced" in your application.

Cheers, Wayne
 

Tee Jay

New Member
Messages
28
Reaction score
0
Points
1
Location
Edmonton
Thanks Wayne. I will have a look and see if I can find those somewhere in town. Lowes and HD don't carry them.
 