Wet Vent question for slab foundation

Users who are viewing this thread

Dylan B

New Member
Messages
3
Reaction score
0
Points
1
Location
Phoenix
Two questions. If I’m using 3” for toilet run and 3” vent run, what is the longest run trap to vent for that toilet?

2nd question. Can a lavatory 2.5” run into the 3” toilet run before it connects to wet vent?

I have tried to outline this in the diagram.
Appreciate all the help, this has me stumped. Open to all suggestions.


And yes. I’m replacing the existing pipe and 45 as clearly they are broken and that is why I’ve decided to build an additional bathroom

B33CB7B5-566B-46D1-A4F8-21AD5C026AB9.jpeg F9B8A877-1D4A-4A5F-8A8D-A0E9F8B3C982.jpeg
 

Tuttles Revenge

In the Trades
Messages
4,200
Reaction score
1,451
Points
113
Toilets trap arms in the UPC code are limited to 72" from its vent.. other codes may vary.

UPC (except in washington state) also wants the toilet to be the most down stream fixture in a horizontal wet vented system.

What type of pipe is that under the slab? It looks like concrete to me.
 

Dylan B

New Member
Messages
3
Reaction score
0
Points
1
Location
Phoenix
Toilets trap arms in the UPC code are limited to 72" from its vent.. other codes may vary.

UPC (except in washington state) also wants the toilet to be the most down stream fixture in a horizontal wet vented system.

What type of pipe is that under the slab? It looks like concrete to me.


Even if it’s a horizontal wet vent it has to be the last fixture?

yes, it is cast iron to concrete. I plan on cutting before the clean out cast iron and after the 45 (concrete) and replacing with pvc with Fernco fittings.
I just cannot figure out how to horizontal vent with the direction of the flow and it tying into the main line 3.5 feet below ground.

suggestions?
 

Attachments

  • 152D8755-E327-4713-98E8-9EA3DB9BD6BA.jpeg
    152D8755-E327-4713-98E8-9EA3DB9BD6BA.jpeg
    121.2 KB · Views: 177

Tuttles Revenge

In the Trades
Messages
4,200
Reaction score
1,451
Points
113
Reading that IPC section, the toilet does Not have to be the most downstream fixture. Your drawing would work for that given the limits of trap arms in the code that Reach4 provided.

Im certain that concrete pipe is not approved for burial under a building. Someone likely enclosed a porch there.. I see it occasionally here and have to remove all of the concrete pipe from the envelope of the house if we find it.
 

Dylan B

New Member
Messages
3
Reaction score
0
Points
1
Location
Phoenix
Reading that IPC section, the toilet does Not have to be the most downstream fixture. Your drawing would work for that given the limits of trap arms in the code that Reach4 provided.

Im certain that concrete pipe is not approved for burial under a building. Someone likely enclosed a porch there.. I see it occasionally here and have to remove all of the concrete pipe from the envelope of the house if we find it.


But can the lavatory connect to the toilet run before it connects to wet vent?

Do you have any code that says I would
Have to dig up concrete if it’s existing structure? Technically, the concrete portion of the pipe is under a concrete patio that is not enclosed.

the wall for the new bathroom would technically be on top of the pvc and the pvc/concrete fernco would be outside that wall and under a non enclosed porch. It does have a roof overhang but it is not enclosed.

If you see from the picture, the previous owner had build a storage room over the broken plumbing and I just am trying to convert that storage room to bathroom ( the concrete portion of the pipe is outside of the “storage room” but under the concrete patio slab
 

Reach4

Well-Known Member
Messages
38,892
Reaction score
4,435
Points
113
Location
IL
But can the lavatory connect to the toilet run before it connects to wet vent?
I am not clear on what you are asking.

The lavatory needs to be vented with a real vent or an AAV.
That upsized drain pipe from the lavatory can then wet-vent the toilet .
 

Tuttles Revenge

In the Trades
Messages
4,200
Reaction score
1,451
Points
113
But can the lavatory connect to the toilet run before it connects to wet vent?

Your drawing shows the sink with the vertical dry vent being the most upstream fixture. Downstream the toilet connects and downstream of that the shower connects. Seems fine to me. You're allowed to have one fixture tie in upstream of that dry vented fixture.

Do you have any code that says I would
Have to dig up concrete if it’s existing structure?

Concrete is not an approved material for burial within the envelope of a building. Never has been approved for that and can never be grandfathered in. If its outside then thats where a gray area begins.. but you can argue that if it comes up. Again, I don't know the specifics of your
 