Washing machine/laundry sink - critique

Users who are viewing this thread

Mikha'el

Member
Messages
76
Reaction score
11
Points
8
Location
Texas
Hi all - for some reason every example out there has the sink "downstream" of the WM standpipe.
If you would, please let me know if there's anything amiss with this schematic - using UPC:


laundry.jpg


Thanks,
Michael
 

Reach4

Well-Known Member
Messages
38,798
Reaction score
4,412
Points
113
Location
IL
"1.5" in the lower right and the "2" above, are not compatible. Probable typo.

Lower right needs to be a long sweep.
 

Mikha'el

Member
Messages
76
Reaction score
11
Points
8
Location
Texas
Add a cleanout for the end of run and you're good.
Kitchen sink also gets a cleanout.
Double-checking - am I ok with a 2" san-tee for the WM drain, into a 3" bushing at the floor - or do I need to carry the 3" up?
Trying to keep the washer drain as low as possible.

Not sure how to read the DFU sizing - is it max 10 dfu for a 2" vertical drain (aka stack <3 stories)?
Do the kitchen sink and dishwasher count as 4 dfu?

EDIT: found it

InkedUPC Table 7-5.jpg



Thanks,
Michael
 