Understanding bull headed tees and flow supplied from branch

Users who are viewing this thread

Rossn

Member
Messages
365
Reaction score
17
Points
18
Location
Denver, CO
For domestic water plumbing is it considered acceptable to have supply flow enter a standard tee from the branch side? Maybe it is location dependent (fixture supply, at a double lav vanity versus at a main branch)?

I was taught by an old-school hydronics guy that a bull headed tee was when the flow entered from the branch side (no reference to a larger branch than run)... and it seems that per IMC 1206.1.1 - in hydronics flow is not allowed to enter through the branch. He seemed to think one should not enter the branch in domestic water plumbing, either.

It seems that plumbers not working in hydronics refer to a bull headed tee as one with a larger branch than the runs.

I saw an example in the IPC that showed flow coming into the branch of a standard tee.
 
Last edited:

Rossn

Member
Messages
365
Reaction score
17
Points
18
Location
Denver, CO
Thanks, Sylvan. Do you lump into that comment using a standard tee with flow in through the branch, or just the tee with the larger branch?
 

Mr tee

In the Trades
Messages
354
Reaction score
145
Points
43
Location
Montana
I never hesitated to use a bullhead tee (of either definition) when if simplified the design of a water or gas system.
 

Gsmith22

Active Member
Messages
234
Reaction score
51
Points
28
Location
Central NJ
all fittings have pressure losses. You can kind of idealize the pressure loss to be similar to two 90 degree bends if flow is coming in through the branch side splitting into flow to the left and right. Its obviously worse than two single 90 degree bends because you don't have the outer pipe wall guiding the flow around a turn. The flow dead ends into the perpendicular wall so if there is a reason to avoid its probably that. The result is a lot of turbulence and resulting pressure loss trying to get the flow to change direction after it smacks into the pipe wall. If a tee with flow coming in through the branch is what works for the layout, I don't see why it would be frowned upon other than recognizing that it will be a big pressure loss and potentially with high enough velocity, maybe there is an erosion issue where the flow dead ends into the pipe wall? Its certainly not the most flow friendly method of plumbing.
 

Rossn

Member
Messages
365
Reaction score
17
Points
18
Location
Denver, CO
thanks all for confirming while best to avoid, not an absolute no-no when it comes to less critical areas (i.e. further down the branch). It sounds like this is a more sensitive topic in hydronics, where pumps may be triggering on and off, and varying flow.

Agreed with gsmith22 that the losses are from the flow being less laminar, and more turbulent in nature, but good to know it isn't known to lead to certain failure/problems, etc.

Thanks for weighing in!
 

wwhitney

In the Trades
Messages
6,532
Reaction score
1,822
Points
113
Location
Berkeley, CA
Some info from the Copper Tube Handbook is below.

It doesn't explicitly give the equivalent feet for the "bullhead" path through a tee. But I think we can assume it is at least the same as the "side branch" equivalent length, maybe even more. Which in all cases is notably more than the 90 degree ell equivalent length.

So it would appear that if you have a supply you wish to split into two, with each heading out at 90 degrees, there's an advantage to using a tee normally, with a 90 degree elbow on the straight outlet.

But if you need the split supplies to be geometrically on the same line, the bullhead tee is obviously much simpler. And while the data below gives a presumable lower bound on the hydraulic "cost" of doing that, I haven't found any explicit data on the equivalent length for a tee in a bullhead configuration.

Cheers, Wayne


Capture.JPG
 

Sylvan

Still learning
Messages
2,756
Reaction score
689
Points
113
Location
New York
Thanks, Sylvan. Do you lump into that comment using a standard tee with flow in through the branch, or just the tee with the larger branch?

Not so much with a standard tee.

The velocity increase through the smaller piping can cause excessive noise and in copper especially on hot water erosion is possible because of the increased turbulence the water goes from big to small just like a reducing ell
 

Jeff H Young

In the Trades
Messages
8,766
Reaction score
2,168
Points
113
Location
92346
I've bull headed water and gas a million times I still wont hesitate on gas. Changed my ways a little and on certain piping I'll avoid the bullhead especially working for other contractors. there are a long list of practices that you never know how others will approve and sometimes I don't want to rock the boat defend why I do it a certain way, like putting an ice maker box in upside down . You'll get chastised for wasting fittings and time coming down from the top and wasting 2 90s or called an idiot for putting it on upside down , something is going to happen to the valve stem sediment or something can't win
 

Rossn

Member
Messages
365
Reaction score
17
Points
18
Location
Denver, CO
Thanks, guys! Clearly not a right or wrong, thing, but avoid when reasonable.

One of the things that prompted the question after thinking I should not do this was the below example from IPC (2015, 2018) Section E103. They actually show the configuration of flow coming in the branch of the tee, which had me scratching my head after hearing from the hydronics old timer to not do that.

Walking their example (which seems to have a few errors), it seems like using straight run vs. side branch length equivalents is not based on where the flow exits the tee (both places), rather where it is entering the tee. Do I have that right? Branch length equivalents for side branch is for when flow enters the side branch as we have been discussing, not when it exits the side branch, as one of the two directions?

upload_2021-4-15_20-55-46.png
 
Last edited:

Rossn

Member
Messages
365
Reaction score
17
Points
18
Location
Denver, CO
I haven't found any explicit data on the equivalent length for a tee in a bullhead configuration.

By 'Bullhead configuration' do you mean a tee with a physical larger branch, or do you mean flow coming in the branch (of a normal tee)?
 

Sylvan

Still learning
Messages
2,756
Reaction score
689
Points
113
Location
New York
bullhead means flow enters the side of the tee
The Supply on a bull head is ALWAYS from the bigger side (BULL) and branches out to the branches


Reading a tee is run first then the middle

BULL head only means the run is smaller then the middle.

Why go from small to big inless your using venting or drainage

3/4 x 3/4 x 1 = Bull tee

3/4 x 1/2 x 3/4 Heel tee

3/4 x 1/2 /x 1/2 reducing tee

3/4 x 3/4 x 1/2 "
 

Sylvan

Still learning
Messages
2,756
Reaction score
689
Points
113
Location
New York
Thanks, Sylvan. Do you lump into that comment using a standard tee with flow in through the branch, or just the tee with the larger branch?
If you use a standard tee and use the middle for the supply it is the same restriction as using a 90 deg ELL (Friction loss)

Coming off a main for example or riser the "branch" most of the time comes off the middle of the tee
Very seldom does the middle supply the main or risers
 

Jeff H Young

In the Trades
Messages
8,766
Reaction score
2,168
Points
113
Location
92346
The Supply on a bull head is ALWAYS from the bigger side (BULL) and branches out to the branches


Reading a tee is run first then the middle

BULL head only means the run is smaller then the middle.

Why go from small to big inless your using venting or drainage

3/4 x 3/4 x 1 = Bull tee

3/4 x 1/2 x 3/4 Heel tee

3/4 x 1/2 /x 1/2 reducing tee

3/4 x 3/4 x 1/2 "
I at times tell a guy EX. Cut me a piece of 3/4 and bullhead the tee . so its not always refering to the type tee but how its installed can have meaning.



If you use a standard tee and use the middle for the supply it is the same restriction as using a 90 deg ELL (Friction loss)

Coming off a main for example or riser the "branch" most of the time comes off the middle of the tee
Very seldom does the middle supply the main or risers
I used to bullhead often I pretty much taught myself in the trade and as career changed found myself under strictor supervision and scrutiny . and had numerous "superiors " tell me not to or that bullheading was undesireable.
So what about if Im running copper water line and install a 2x2 x1/2 tee because im picking up something small . whats the differance which way I feed that tee ? from the bull or heel whats the differance ? My way of thinking I want less turns .
So Ive had to go with how I was told or how I see others not really what My gut thinks is better just follow convention.
If Im running down a joist bay and then need to go right and left (2 opposite directions ) why not bullhead it just never made sence not to. and this isnt uncommon at all unless you work in high rise But One and 2 floors its common
 

Fitter30

Well-Known Member
Messages
4,292
Reaction score
778
Points
113
Location
Peace valley missouri
Devil s advocate. How often have you come across copper erosion from turbulence. How many swing joints with 90° and st90° have you installed.
Even with 90lbs - 100lbs of city water pressure. Might be hard of faucets and solenoid valves. High rise office and apartment buildings using booster pumps. Architects and engineers give the mechanical systems as little room as possible and sometimes just have to make the space work.
 

Tuttles Revenge

In the Trades
Messages
4,132
Reaction score
1,410
Points
113
The Supply on a bull head is ALWAYS from the bigger side (BULL) and branches out to the branches


Reading a tee is run first then the middle

BULL head only means the run is smaller then the middle.

Why go from small to big inless your using venting or drainage

3/4 x 3/4 x 1 = Bull tee

3/4 x 1/2 x 3/4 Heel tee

3/4 x 1/2 /x 1/2 reducing tee

3/4 x 3/4 x 1/2 "
To illustrate what Sylvan wrote:

1708102225550.png
 

Jeff H Young

In the Trades
Messages
8,766
Reaction score
2,168
Points
113
Location
92346
Devil s advocate. How often have you come across copper erosion from turbulence. How many swing joints with 90° and st90° have you installed.
Even with 90lbs - 100lbs of city water pressure. Might be hard of faucets and solenoid valves. High rise office and apartment buildings using booster pumps. Architects and engineers give the mechanical systems as little room as possible and sometimes just have to make the space work.
I installed swing joints but havent experianced a lot of issues . sure its gotta be harder.
But In regards to bullhead tees I dont see why turbulance going through a tee such as a 1 1/2 x1/2 x1 1/2 would vary whether flow is from side or heel . I sure dont know enough about physics to say they are equall I might even be suprised to hear that coming in from side is less turbulant than a reducing tee scenario. In a continuously flowing system I think it would make a bigger differance than say potable water on a house
 