Main from meter seems to be (3/4) refrigerant line... looking to replace PRV and need help..

Users who are viewing this thread

Max Frisbee

New Member
Messages
7
Reaction score
0
Points
1
Location
Chattanooga, Tn.
Hey guys, so I was all ready to have a nice little project here at home replacing a very old (65’ manufacture date) PRV with a new one and also fix some funky reducers and extra fittings that are unnecessary just past the PRV.

I came to find out that my 3/4 quick cut doesn’t cut the line that I thought was 3/4. It is a decent amount smaller (not 1/2” though). I called a plumbing friend and he said it was likely refrigerant line. Currently the “refrigerant line” couples down to what looks like 1/2” hard copper with a sweat reducer.

I have all my supplies set up to convert the 1/2” line that was reduced off what I thought was 3/4 copper with a 3/4 ball valve (wirsbo), Watts Aub25 with my male wirsbo adapters and some PEX to take over to the water heater.

what is the simplest solution to still do this? Can I go from 3/4 (or what ever this actually is) refrigerant line to 3/4 hard copper so that I can run all my current supplies I’ve gathered... or would increasing to 3/4 have ill affects since it’s larger diameter than the main. If so I can just return the stuff I have and use the 1/2” hard that is already soldered and reduced from the main.
 

Max Frisbee

New Member
Messages
7
Reaction score
0
Points
1
Location
Chattanooga, Tn.
Here is a shot of what’s here along with a funky double PRV? ‍♂️

1D307A2F-DADC-4F08-9A3F-0D3CFBD4AC6E.jpeg
 

James Henry

In the Trades
Messages
1,578
Reaction score
403
Points
83
Location
Billings, Montana.
What a mess, somebody obviously used what ever parts they could scrounge. The minimum residential main water line needs to be 3/4", cut back all the way to where it starts at 3/4" and use a 3/4" PRV and ball valve and 3/4" to the water heater.
 

Max Frisbee

New Member
Messages
7
Reaction score
0
Points
1
Location
Chattanooga, Tn.
The sad part is that the refrigerant line to the road is down the side of a mountain and it would be hell to replace. Is there a viable solution to use the (slight less than) 3/4(?) refrigerant line that is stubbed out in the crawl space and connect it 3/4 hard copper or PEX?
 

Reach4

Well-Known Member
Messages
38,861
Reaction score
4,429
Points
113
Location
IL
The sad part is that the refrigerant line to the road is down the side of a mountain and it would be hell to replace. Is there a viable solution to use the (slight less than) 3/4(?) refrigerant line that is stubbed out in the crawl space and connect it 3/4 hard copper or pex?
I think you should stop using terms like "(slight less than) 3/4(?) refrigerant line " and measure to 0.001 inches. Do you know what you need to measure that?

63711_W3.jpg
 

Paulypfunk

In the Trades
Messages
66
Reaction score
28
Points
18
Location
Seattle
I’m guessing that is 5/8” ID refrigeration tubing with ‘flare’ fittings. Kind of hard to say from the one picture you posted. We use a little swedge tool to make little trumpet flares on the end of the copper which is then compressed onto cone shaped fittings. Pretty obsolete these days but nothing really wrong with it.
We base the size of the pipe that should be in your house based on the number of plumbing fixtures and how much water they use but 3/4” ID is the minimum and has been for a while now. If you replace the PRV I would upsize the pipe downstream of the apparatus, no problem with going bigger.
 

Max Frisbee

New Member
Messages
7
Reaction score
0
Points
1
Location
Chattanooga, Tn.
Hey.... I’m learning hahah. Finally got around to buying this fancy fella!

that is the outside diameter of the line that I would like to attach to and clean up all the random junk on the main in line... hopefully to 3/4
 

Attachments

  • 767CE7E6-83D2-4D26-9511-84B62570B808.jpeg
    767CE7E6-83D2-4D26-9511-84B62570B808.jpeg
    108.5 KB · Views: 176

Tuttles Revenge

In the Trades
Messages
4,179
Reaction score
1,440
Points
113
What is the fitting below the PRV at the bottom of the picture? Is that a flare X threads that thread into the PRV? Can you start there with a new threaded ball valve, then install a tee with a boiler drain, then your new PRV then connect to the PEX with something other than the sharkbite?
 

Attachments

  • Water Main.png
    Water Main.png
    145 KB · Views: 186

Max Frisbee

New Member
Messages
7
Reaction score
0
Points
1
Location
Chattanooga, Tn.
What is the fitting below the PRV at the bottom of the picture? Is that a flare X threads that thread into the PRV? Can you start there with a new threaded ball valve, then install a tee with a boiler drain, then your new PRV then connect to the PEX with something other than the sharkbite?

problem with that is that it comes in on that .76 OD line then reduces down to 1/2” PRV and such. I’ve already secured a new PRV and ball valve 3/4” because I thought it would be a easy swap over since I have access to a Wirsbo tool and such.
 