Double vanity and laundry in 2" PVC

Users who are viewing this thread

Alfred

New Member
Messages
4
Reaction score
0
Points
1
Location
Dallas, TX
I am in the process of remodeling a bathroom and would like to add laundry to the same room. The only drain available to me is a 2" line that is currently being used just for the vanities. I would like to add the laundry, be up to code, and not have to replace anything under the slab. I would appreciate any help you could give. I am located in Texas.

Current:
- 2" PVC drain to slab w/ 1.5" vent stack
- 2x Vanity w/ 1.5" drains to double sanitary tee to main 2" drain to slab

Propose:
- keep current configuration above
- add 2" drain for laundry that feeds into a sanitary tee below current vanity double tee
- add 2" vent stack just for the laundry


plumbing_config.jpg
 
Last edited:

wwhitney

In the Trades
Messages
6,532
Reaction score
1,822
Points
113
Location
Berkeley, CA
I am in the process of remodeling a bathroom and would like to add laundry to the same room. The only drain available to me is a 2" line that is currently being used just for the vanities. I would like to add the laundry, be up to code, and not have to replace anything under the slab.
That's not possible under the IPC, because of the requirement that the drain for the clothes washer standpipe increase to 3" as soon as it joins another drain. Third sentence in 406.2:

https://up.codes/viewer/texas/ipc-2015/chapter/4/fixtures-faucets-and-fixture-fittings#406.2

Are you perhaps in a jurisdiction that uses the UPC? I have a vague recollection some cities in Texas do, but I may be mistaken.

Under the UPC, your proposed drawing is fine. (18" is the maximum height of the standpipe trap above the floor, where to measure that to is unspecified. 6" is the minimum.) The laundry vent doesn't need to be 2", it could be 1.5".

Also under the UPC, if you want, the laundry doesn't need a separate vent, it could be wet vented by the double lav. You'd lower the trap so its outlet can hit a 2" san-tee below your double lav san-tee.

Cheers, Wayne
 

Reach4

Well-Known Member
Messages
38,795
Reaction score
4,413
Points
113
Location
IL
Are you perhaps in a jurisdiction that uses the UPC? I have a vague recollection some cities in Texas do, but I may be mistaken.
I think Dallas is not in the list of UPC in Texas.

That's not possible under the IPC, because of the requirement that the drain for the clothes washer standpipe increase to 3" as soon as it joins another drain.
If Alfred had installed that per his drawing before the 2015 IPC was adopted by Texas, it would have continued to work great into the future.

Alfred, maybe you could ask for an exception.
 

Alfred

New Member
Messages
4
Reaction score
0
Points
1
Location
Dallas, TX
That's not possible under the IPC, because of the requirement that the drain for the clothes washer standpipe increase to 3" as soon as it joins another drain. Third sentence in 406.2:

https://up.codes/viewer/texas/ipc-2015/chapter/4/fixtures-faucets-and-fixture-fittings#406.2

Are you perhaps in a jurisdiction that uses the UPC? I have a vague recollection some cities in Texas do, but I may be mistaken.

Under the UPC, your proposed drawing is fine. (18" is the maximum height of the standpipe trap above the floor, where to measure that to is unspecified. 6" is the minimum.) The laundry vent doesn't need to be 2", it could be 1.5".

Also under the UPC, if you want, the laundry doesn't need a separate vent, it could be wet vented by the double lav. You'd lower the trap so its outlet can hit a 2" san-tee below your double lav san-tee.

Cheers, Wayne

Thank you Wayne,

In my city we are under the IPC 2015 as of right now. I appreciate the input and will try to figure out another solution that will meet the IPC standards. Hopefully nothing too drastic.
 

wwhitney

In the Trades
Messages
6,532
Reaction score
1,822
Points
113
Location
Berkeley, CA
If Alfred had installed that per his drawing before the 2015 IPC was adopted by Texas, it would have continued to work great into the future.
The requirement is in the 2012 IPC. I remember looking up what year it was added to the IPC, but I don't remember the answer. : - )

Cheers, Wayne
 

wwhitney

In the Trades
Messages
6,532
Reaction score
1,822
Points
113
Location
Berkeley, CA
In my city we are under the IPC 2015 as of right now. I appreciate the input and will try to figure out another solution that will meet the IPC standards. Hopefully nothing too drastic.
Well, your two options under the 2015 IPC are (1) use a laundry tub or (2) find a 3" drain line to bring the laundry standpipe fixture drain to.

[Fixture drain means a drain serving only one fixture.]

Cheers, Wayne
 

Alfred

New Member
Messages
4
Reaction score
0
Points
1
Location
Dallas, TX
Well, your two options under the 2015 IPC are (1) use a laundry tub or (2) find a 3" drain line to bring the laundry standpipe fixture drain to.

[Fixture drain means a drain serving only one fixture.]

Cheers, Wayne

Just to make sure I am understanding you correctly if the drain line that penetrates the slab was 3" instead of the current 2" right before it goes into the long sweep it would meet the IPC 2015 rules? I will need to verify what size line runs under the slab that feeds this line.

Thanks,
Alfred
 

wwhitney

In the Trades
Messages
6,532
Reaction score
1,822
Points
113
Location
Berkeley, CA
Just to make sure I am understanding you correctly if the drain line that penetrates the slab was 3" instead of the current 2" right before it goes into the long sweep it would meet the IPC 2015 rules?
Yes, if the vertical pipe segment just above the slab were 3", then you could install a 3" x 2" san tee or combo to bring the laundry standpipe drain in, and that would be compliant with IPC 406.2.

So if there's a horizontal 3" line under the slab near your wall, you can break up some concrete and tie in the laundry fixture drain there instead of in the wall, and that complies with IPC 406.2. Personally, I'm not sure I believe in the IPC requirement enough to break up concrete to comply with it, but I live in a UPC jurisdiction, so I wouldn't have to make that decision.

Note that under the IPC, I don't believe you can do wet venting with two lavs over a laundry standpipe, so you do need the separate standpipe vent. But the vent still only has to be 1.5".

Cheers, Wayne
 
Last edited:

Alfred

New Member
Messages
4
Reaction score
0
Points
1
Location
Dallas, TX
Yes, if the vertical pipe segment just above the slab were 3", then you could install a 3" x 2" san tee or combo and be compliant with IPC 406.2.

So if there's a horizontal 3" line under the slab near your wall, you can break up some concrete and tie in the laundry fixture drain there instead of in the wall, and that complies with IPC 406.2. Personally, I'm not sure I believe in the IPC requirement enough to break up concrete to comply with it, but I live in a UPC jurisdiction, so I wouldn't have to make that decision.

Note that under the IPC, I don't believe you can do wet venting with two lavs over a laundry standpipe, so you do need the separate standpipe vent. But the vent still only has to be 1.5".

Cheers, Wayne


I will scope the line and see how easy it is and make the decision at that time. Thank you for guiding a novice through the intricacies of the code.
 

Reach4

Well-Known Member
Messages
38,795
Reaction score
4,413
Points
113
Location
IL
Well, your two options under the 2015 IPC are (1) use a laundry tub or (2) find a 3" drain line to bring the laundry standpipe fixture drain to.
1. Was 2015 the IPC version that introduced that 3-inch requirement? If the standpipe had been installed before the code was adopted, it would have been allowed to remain. If it were mine, I might ...

2. I would think that local code authorities might be willing to make an exception where replumbing to 3-inch would be a hardship. After all, UPC is still OK with 2 inch having standpipe and some other drainage in it.

3. If you put in a laundry sink, and empty the washer into that, then 2 inch is still allowed.
 

Tuttles Revenge

In the Trades
Messages
4,132
Reaction score
1,410
Points
113
I would be tempted to ask for an exemption or use an "alternative method" .. I have gotten exemptions for upsizing a drain from 3" to 4" when adding a 4th toilet on a horizontal drain because there was too much disruption of concrete to upsize the drain. There are millions of installations of laundry on 2" and plenty of codes where its obviously acceptable as evidence.
 