Boiler Overflow and Auto Bleeder Issue

Users who are viewing this thread

velosnow

New Member
Messages
14
Reaction score
0
Points
1
Location
Colorado
You guys have been super helpful in the past and I'm back with a fresh issue in a new house. Bought a 1960's fixer last year and we have baseboard heaters coupled with a boiler. No experience with either really and have a couple questions.

1 - In our small bathroom an air vent (at least I think that's what it is) has apparently been leaking for a long time. Finally got around to the planned demo and discovered subfloor damage so it's been doing it awhile. Question is, how do I replace it? Or can I just tighten the cap? Do I need to bleed the system if I replace it? This one might be over my head so any estimates on getting someone out is appreciated.

2 - Our boiler has a bucket next to it that has been overflowing. Just noticed it a couple of weeks ago and assumed it just needed dumped from the winter. So I ran it outside, dumped it and put it back. Since then the boiler has maybe ran 3 hours and it already overflowed. Again, no idea what I'm really looking at. Normal? Not normal? It's about 18 years old and our home inspector said they can last a long time but indicated it's toward the end of average lifetime if memory serves.

Thanks again!

i-69mGGwS-XL.jpg


i-dBxkK7V-XL.jpg


i-wp2s7cb-XL.jpg
 

Fitter30

Well-Known Member
Messages
4,290
Reaction score
777
Points
113
Location
Peace valley missouri
Auto air bleed just unscrews 1/8" pipe thread. System has to be drained for replacement. Might want to look at other baseboards there air bleeds you might want to change. Boiler water pressure should run 10 - 12 lbs cold. If the expansion tank bladder is bad - no air pressur or if the type of tank is just a tank it could be full of water when boiler temperature comes up pressure in the boiler will rise quickly till pressure gets to 30 lbs and relief valve will leak. Post some more pics of the bliler , pump and expansion tank.
 

velosnow

New Member
Messages
14
Reaction score
0
Points
1
Location
Colorado
Auto air bleed just unscrews 1/8" pipe thread. System has to be drained for replacement. Might want to look at other baseboards there air bleeds you might want to change. Boiler water pressure should run 10 - 12 lbs cold. If the expansion tank bladder is bad - no air pressur or if the type of tank is just a tank it could be full of water when boiler temperature comes up pressure in the boiler will rise quickly till pressure gets to 30 lbs and relief valve will leak. Post some more pics of the bliler , pump and expansion tank.

Thanks, I'll get back down there for some more pics tomorrow. Here is one of the tank...

i-JVJ4VQS-XL.jpg
 

Fitter30

Well-Known Member
Messages
4,290
Reaction score
777
Points
113
Location
Peace valley missouri
That tank is a bladder style expansion tank the blue cap at the bottom is for the air charge. It's a schrader valve (tire valve). For service need a low pressure air gauge 0-50 lb or lower pressure and either air compressor or hand pump.
With boiler off cold or under 120* depress schrader just for a second if water comes out bad tank, air charge should be same as water pressure 10-12 lbs single story house. Need pic of the pump with the relationship with the pump.
 

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,771
Reaction score
1,191
Points
113
Location
New England
If your boiler safety pressure relief valve has been opening regularly (it normally should NOT open except in an emergency), then once you fix the reason why it had to open, you should replace it with a new one.

Heating water expands it, so the expansion tank is critical to absorb that extra volume and keep the pressure within normal range. That tank needs to be sized properly, pre-charged properly, and not water-logged (i.e., failed) for it to work. What pressure you should have in your boiler depends somewhat on the internal controls (mine won't fire unless it is over 12-psi) and how tall the building is with regards to the piping. Pressure drops about 0.43-psi per foot...you need the top of the run to be above zero to keep it from creating a vacuum, and lowering the boiling pressure of the water in the boiler.

FWIW, the ET normally doesn't really get all that hot, so insulating it may not gain much benefit, and it could trap moisture that could start to rust it from the outside.

If you're lucky, you can just depressurize the heating system and pump up the old ET, but it's likely that it will need replacement. Pre-charge it to your system pressure before installation.

I'd change that air bleeder while I had the system drained enough to open that up without water spilling everywhere.
 

Dana

In the trades
Messages
7,889
Reaction score
509
Points
113
Location
01609
Replacing the bleeders and any leaking vents would be a good start, as well as calculating then verifying the correct system pressure and pre-charge on the expansion tank.

Even when derated for altitude a 162K-in /132K-out boiler is likely to be RIDICULOUSLY oversized for the actual design heat load, and might even be oversized for the amount of baseboard. Most 18 year old boilers have plenty of life left in them, but if it's 4x+ oversized for the design load or crazy oversized for the radiation it might be worth retiring it early. Run a fuel-use based load calculation to get a baseline number for the "before tightening & insulating" condition of the house.

How much baseboard total is there in the house? (If controlled as multiple zones, break it down zone by zone.)

What is your elevation?
 

velosnow

New Member
Messages
14
Reaction score
0
Points
1
Location
Colorado
Ok guys, appreciate the responses so far and sorry to be slow. Had to move onto other projects for a minute but circling back as I'm getting ready to tackle this.

Had a local guy come out last week who is the company's go to guy for boilers. First thing he noticed is that it isn't up to code - top of it is 11" away from floor joist not the 18" required - and thus won't work on it. That said, he graciously took his time to show me what I needed to do though I wasn't prepared to take notes. He also gave me a quote for a combined boiler/hot water heater and that ain't cheap. So I'd like to keep this system around for now.

So going forward my plan is to actually remove the baseboard heater portion in that tiny bathroom altogether and either put electric radiant floor heat or different small heating source in. I plan to drain the system, remove the troublesome vent along with the the heater and simply continue the loop below the floor with some fresh pipe.

Also apparently my Extrol tank is indeed bad so I'll be ordering a new one to replace along with likely a pressure relief valve.

Here are my initial thoughts, let me know if any of these are not needed or in the proper order:

1) shut off breaker
2) close shutoff valve from supply (blue circle)
3) open system to drain it via bottom valve (yellow circle)
> how much water is in here anyway? thinking of putting a hose on and filling buckets as needed to carry out
4) replace pressure relief valve (red circle)
5) remove the bad vent/baseboard heater and replace with continued loop under floor
6) remove & replace Extrol tank
7) double check all fittings
8) close system
9) breaker on
10) open supply valve and see how I did
smile.gif


Lastly, will the system need to be bled afterward? I think that's it for the moment, again appreciate the responses!

i-NdRpd9V-X2.jpg
 

velosnow

New Member
Messages
14
Reaction score
0
Points
1
Location
Colorado
Replacing the bleeders and any leaking vents would be a good start, as well as calculating then verifying the correct system pressure and pre-charge on the expansion tank.

Even when derated for altitude a 162K-in /132K-out boiler is likely to be RIDICULOUSLY oversized for the actual design heat load, and might even be oversized for the amount of baseboard. Most 18 year old boilers have plenty of life left in them, but if it's 4x+ oversized for the design load or crazy oversized for the radiation it might be worth retiring it early. Run a fuel-use based load calculation to get a baseline number for the "before tightening & insulating" condition of the house.

How much baseboard total is there in the house? (If controlled as multiple zones, break it down zone by zone.)

What is your elevation?

I'm right at 5,280' and it is one zone with about 65' of baseboard heater.
 

Dana

In the trades
Messages
7,889
Reaction score
509
Points
113
Location
01609
65' of typical baseboard emits about 40,000 BTU/hr at an average water temp of 180F (190F out, 170F return). It's probably short cycling a bit, maybe even quite a bit if the house is broken up into multiple zones with independent thermostats. With a sea-level rating of 132,000 BTU/hr of DOE output (derates to about 100KBTU/hr at your altitude) that boiler really is crazy oversized for your 65' of baseboard, on the order of 2.5x oversized even for the radiation (even when derated), and likely more than 3x the design heat load of a normal sized house, clearly way more boiler than you can ever use. Retrofitting a HydroStat 3250 or similar would be cost effective if you're keeping it.

You don't need to drain the system to work on the radiation or the expansion tank. Just locate a bleeder valve on the first floor, crack it open a bit, and drain until it starts sucking a bit of air. Assuming it's all on one level and about 100' of 3/4" plumbing (including baseboards) at that level it's only a couple of gallons.

If the expansion tank can be isolated with a valve, the system doesn't need to be drained at all for that step. If it can't be isolated, start unscrewing it and drain only until the dripping stops.

As part of step #6, calculate the required system pressure, and pump up the air pressure to that amount +1 psi BEFORE installing it. Typically going with the minimum 12 psi is fine for single or two story homes with the boiler in the basement. Don't set the system pressure below 12 psi at the boiler since that increases the risk of kettling on the boiler plates &/or cavitation on the pumps.

If the pressure relief isn't dripping between burner firings, but only when the system pressure is reading north of 25 psi it's just fine, doing it's job, and would not need to be replaced.

After your step #8, leave the breaker off, turn the filler valve open, and fill the system to the pressure calculated for step #6, turn the isolating filler valve off, then go bleed air at the baseboard vents. The system pressure will drop when the air gets bled, so this step should be repeated. Alternatively ,adjust the auto-fill valve after adjusting it to the proper system pressure, and trust it to add water to keep the pressure up as the radiators get bled to where they're only delivering water, not hissing or sputtering air.

Only THEN would it be time to turn the breaker back on.
 

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,771
Reaction score
1,191
Points
113
Location
New England
FWIW, the boiler I have won't fire if the pressure is below 12psi...so, they recommend about 15psi to give a little room. Yours may not have a low-pressure interlock switch...mine does.
 