Hot water tank tripping reset

Users who are viewing this thread

Plumber69

In the Trades
Messages
2,380
Reaction score
214
Points
63
Location
Prince Rupert, British Columbia
Tank is 2 years old, elements tested ok for continuity, even drained tank and inspected them. Water gets extremely hot then trips. I changed the bottom element, going see what that does. I heard if an element fails it will still continue to heat water at a lower votage. If thats the case I may have changed wrong element
 

Fitter30

Well-Known Member
Messages
4,289
Reaction score
777
Points
113
Location
Peace valley missouri
Your amp draw is 9 amps you don't add both wire reading going to 1 element. 5500watts @ 240 vac 22.9 amps
Watts divided by by volts. Did you check voltage across element?
 

Fitter30

Well-Known Member
Messages
4,289
Reaction score
777
Points
113
Location
Peace valley missouri
10.5 ohms with wires off is 5500 watt element. Double check name tag on element sounds like wrong voltage. Compare to other element.
 

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,771
Reaction score
1,191
Points
113
Location
New England
You're getting 9*240= 2160W (more or less depending on your actual voltage), which seems low, but could be okay depending on the actual element used. It's not 18A. All of the current that goes in one side, goes out the other, so they don't add as was said. Essentially, you're measuring along the same wire. It gets a bit more complicated if it's a 3-phase circuit, but essentially, it's a one-phase. 120vac is sort of a fake result of the way the power is supplied. You're actually being supplied with 240vac with a middle tap (neutral) from the transformer.

Using and understanding test equipment is critical to getting good indications. Heating elements tend to short or open when they're not working right. Their actual cold resistance will change a bit as they heat up, but will give you a good rough idea you can test. Just make sure the power is off and you've removed the incoming wires.
 

Gagecalman

Active Member
Messages
160
Reaction score
35
Points
28
Location
Baltimore, MD
It sounds like a thermostat issue.
If the thermostats are working correctly, they will cut power to the element in use when the set temperature is reached.
 

Reach4

Well-Known Member
Messages
38,795
Reaction score
4,413
Points
113
Location
IL
So i should get 22.9 amps on both wires. If im only getting 9 amps but 240 volts, what is issue
Bad element, or bad meter.

EDIT: you are clamping around one wire at a time, right? If you clamp around both, you should read zero normally.
 
Last edited:

Gagecalman

Active Member
Messages
160
Reaction score
35
Points
28
Location
Baltimore, MD
top thermostat was changed
Have you checked the lower?

I don't understand how the elements are getting power if the thermostats are working properly. If they are set to 120° and the water is getting extremely hot and you still have power going to the elements then there has to be something wrong with the thermostats or the way they are wired.
 

JerryR

Active Member
Messages
584
Reaction score
41
Points
28
Location
Florida
Bad element or bad thermostat.

With power off and wires disconnected to the elements Ohm out the elements across the screw contacts and Ohm out each screw to the water heater inner case.

A shorted element WILL heat up water slowly until the overtemp trips.

Element will always have power to one connection. When thermostat calls for heat the thermostat puts power to the other connection. A shorted element can have a short to ground and therefor be powered with 120 volts and slowly heat up water until the overtemp on the top thermostat trips.
 