Furnace burner and blower take turns

Users who are viewing this thread

SShaw

Member
Messages
53
Reaction score
14
Points
8
Location
Virginia
Sounds like the limit switch is cutting off the burner. The furnace could be overheating, or the limit switch could be set wrong, or gone bad.
 

Plumber69

In the Trades
Messages
2,380
Reaction score
214
Points
63
Location
Prince Rupert, British Columbia
Sounds like the limit switch is cutting off the burner. The furnace could be overheating, or the limit switch could be set wrong, or gone bad.
Jumped the limit switch, blower wouldn't come on. All I can think is its this thing
 

Attachments

  • 20191204_100552.jpg
    20191204_100552.jpg
    77.3 KB · Views: 156

SShaw

Member
Messages
53
Reaction score
14
Points
8
Location
Virginia
I don't know what that thing is in the photo.

All I know is the limit switch has several functions which would be consistent with the behavior you saw. It will: 1) turn the fan ON after the burner starts and the HX gets hot enough, 2) keep the fan ON after the burner is off to remove excess heat from the HX, 3) turn the fan OFF after the HX cools down too much, and 4) cut off the burner OFF if the HX gets dangerously hot.

You should get an HVAC tech who knows oil to diagnose things. You don't want to take chances with oil.
 