I understand the concept of friction when going from a larger pipe diameter to small. However, what happens in reverse?

For example, I have a well pump that has a 1 inch output and I have 1 1/4 sprinkler lines coming of that 1 inch pipe.

Since the well pump has 1 inch output does that mean I will never get to use the extra friction room that a 1 1/4 pipe gives over a 1 inch pipe?

Basically it goes: Suction up the well water via the pump at 1 1/4. Then go through the pump and then discharge out of the pump orriface at 1 inch. It gets imediatley converted to a 1 1/4 pvc going out to various devices. Is the 1 1/4 pipe useless after the 1 inch discharge?

Thanks all
 

Reach4

Well-Known Member
Messages
38,892
Reaction score
4,435
Points
113
Location
IL
Is the 1 1/4 pipe useless after the 1 inch discharge?
No. The pressure drops add. The one inch section has a drop. Then the 1-1/4 section has a drop. It's not like road traffic where the slowest section determines the throughput.
 

stormlight

New Member
Messages
24
Reaction score
0
Points
1
Location
CA
So if im understanding since there is less then an inch of 1 inch pipe in this run (it gets converted from the 1 inch output to 1 1/4 pipe right at the pump) I can pretty much ignore the friction from the 1 inch pipe since its so small.
 

Valveman

Cary Austin
Staff member
Messages
14,633
Reaction score
1,303
Points
113
Location
Lubbock, Texas
Website
cyclestopvalves.com
No. As Reach said each leg adds additional friction loss. Determine the friction loss in the length of 1" pipe. Determine the friction loss in the actual length of 1 1/4" pipe, and add the two together. You would have even more friction loss if all the pipe was 1".
 

stormlight

New Member
Messages
24
Reaction score
0
Points
1
Location
CA
What I was saying is that the total length of the one inch pipe in this run is less then .5 inches. According to the friction calculator 1 foot of 1 inch sSCH 40 pipe has .31 of pressure loss. If i divide .31/12 that is not even measurable for me. What I was most concerned was for that tiny .5 inch run of 1 inch pipe to be the limiter in the entire run of all my 100 foot four zones that have 1 1/4 pipe size.

It looks like its not and i just need to ad .02 (.32/12 inch) to my friction.
 

Valveman

Cary Austin
Staff member
Messages
14,633
Reaction score
1,303
Points
113
Location
Lubbock, Texas
Website
cyclestopvalves.com
That is correct. You can push a lot of water through a short piece of small pipe without much friction loss. But it you have hundreds of feet of small pipe the friction loss adds up quickly. We can easily push 25 GPM through a short 1" CSV, but you want to go back up to 1 1/4 or larger pipe after that or you will start losing pressure.
 

Reach4

Well-Known Member
Messages
38,892
Reaction score
4,435
Points
113
Location
IL
What I was saying is that the total length of the one inch pipe in this run is less then .5 inches. According to the friction calculator 1 foot of 1 inch sSCH 40 pipe has .31 of pressure loss.
Maybe you chose too high of a flow. Your pump is not going to put out more than about 10 gpm I suspect.

You might try this calculator: http://www.pressure-drop.com/Online-Calculator/ Maybe use 0.1 mm for the roughness.

It has choices of things other than straight runs, such as change of section, although I have not played with those.
 