One last check before I pull the pump, advice needed.

Users who are viewing this thread

James Thomas

New Member
Messages
16
Reaction score
0
Points
1
Location
Missouri
New member here, I've been reading different sites and forums all day, this forum seems the most helpful.

Anyways, a little back history, well is from the 70s-80s, no known depths, most wells around here are in the mid 300ft to 500ft range. All of the above ground parts are 10 years old.

About 4 months ago my automatic shutoff failed ON for at least a month, every since then my pressure has been falling, now when I turn the water on it drops down to about 0-5psi, (still enough pressure for one faucet at a time.) When I turn the water back off the pressure jumps right back up to 50psi (was 60psi but it wouldn't pump that high so I turned the cutout down to shorten the run time)

I just want to make sure that the pump is the problem before I replace.

As far as pumps go, right now my budget is enough for a red lion RL12G15-3W2V
Because I dont know the dept of the well and I'm looking at just pulling and replacing same day/weekend. So I just picked their largest pump. Would their be any Ill effects if my well ends up being shallower?

I was also looking at a company called Schraiber pump, they make one that has about the same performance numbers as the red lion, for a couple hundred cheaper. (They also have great reviews all over on line)
 

Valveman

Cary Austin
Staff member
Messages
14,599
Reaction score
1,296
Points
113
Location
Lubbock, Texas
Website
cyclestopvalves.com
From 300' or less that pump will work. Over 300' it won't build any pressure. Best to know the pump setting and water level depth before purchasing a pump.
 

James Thomas

New Member
Messages
16
Reaction score
0
Points
1
Location
Missouri
From 300' or less that pump will work. Over 300' it won't build any pressure. Best to know the pump setting and water level depth before purchasing a pump.

Hmm.. all the specs on this one said 500ft head lift. That's why I picked it.
I know the pump that is down there now only has a 1hp motor on it(that's what the well company said based off amp ratings they were getting)
Maybe I'm over estimating my depths.
 

Reach4

Well-Known Member
Messages
38,798
Reaction score
4,412
Points
113
Location
IL
For a house, you would probably be better off with a 7 or 10 gpm pump. For a given HP, they have more lift+pressure than a 12 gpm pump.

About 4 months ago my automatic shutoff failed ON for at least a month, every since then my pressure has been falling, now when I turn the water on it drops down to about 0-5psi, (still enough pressure for one faucet at a time.) When I turn the water back off the pressure jumps right back up to 50psi (was 60psi but it wouldn't pump that high so I turned the cutout down to shorten the run time)
That 0 to 5 psi is at the gauge on the pressure tank?

When you refer to turning the water on or off, do you mean opening a faucet, or do you mean turning the power to the pump on and off?

If the faucet, try this experiment. If the pressure is at 50, and you turn off power to the pump, does the pressure hold fairly close to 50? If you then use water from the faucet, briefly, the pressure drops. Now turn the faucet back off. Does the pressure come back up considerably? If so, there may be a restriction rather than a pump problem.
 
Last edited:

Valveman

Cary Austin
Staff member
Messages
14,599
Reaction score
1,296
Points
113
Location
Lubbock, Texas
Website
cyclestopvalves.com
Hmm.. all the specs on this one said 500ft head lift. That's why I picked it.
I know the pump that is down there now only has a 1hp motor on it(that's what the well company said based off amp ratings they were getting)
Maybe I'm over estimating my depths.

60 PSI is the same as 138' of head. So to get a pump that will build 60 PSI from 500', the pump would need to be able to produce 638' of head.

But you also do not want a pump that can produce 638' of head if your well is only 200-300' to water.
 

James Thomas

New Member
Messages
16
Reaction score
0
Points
1
Location
Missouri
That 0 to 5 psi is at the gauge on the pressure tank?

When you refer to turning the water on or off, do you mean opening a faucet, or do you mean turning the power to the pump on and off?

If the faucet, try this experiment. If the pressure is at 50, and you turn off power to the pump, does the pressure hold fairly close to 50? If you then use water from the faucet, briefly, the pressure drops. Now turn the faucet back off. Does the pressure come back up considerably? If so, there may be a restriction rather than a pump problem.

Yes that 0-5psi is at the pressure tank(which is 3 ft from my well pipe)

With power ON
When I turn the faucet on in the well house the pressure drops, but water flows out, and pump kicks on, turn faucet off pressure builds back to 50psi and pump turns off.(builds to 50 in a matter of seconds)

With power OFF
Turn faucet on and pressure drops and water stops flowing, turn faucet off and pressure gauge stays at 0. Turn power back on to the pump and pressure builds back to 50psi

Also I get the same results no matter what faucet I use, be it at the well house, in the fields at the cattle waterers, or in the house)
And I'm not getting any aeration in the water, if that helps.

** note I only have a 1gal pressure tank due to location, will be upgrading to a once I get the new bigger well house build**
 

Valveman

Cary Austin
Staff member
Messages
14,599
Reaction score
1,296
Points
113
Location
Lubbock, Texas
Website
cyclestopvalves.com
1 gallon pressure tank??? Even with a Cycle Stop Valve we recommend a 4.5 gallon size tank. Gonna be hard to get it to work right with a 1 gallon tank. Probably already a bad tank, as that is lots of cycling. Pump build to 50 and shuts off, sounds like the pump is not the problem.
 

James Thomas

New Member
Messages
16
Reaction score
0
Points
1
Location
Missouri
1 gallon pressure tank??? Even with a Cycle Stop Valve we recommend a 4.5 gallon size tank. Gonna be hard to get it to work right with a 1 gallon tank. Probably already a bad tank, as that is lots of cycling. Pump build to 50 and shuts off, sounds like the pump is not the problem.
Went and double checked the numbers it's a well-x-tol wx-102, 4.4gal tank. It looked small so I assumed it was a 1gal.
It holds the 38psi fine, so I figured it was functioning as normal.
Edit* it is in fact a 4.4 gal tank. I had to look up the dimensions
 
Last edited:

Valveman

Cary Austin
Staff member
Messages
14,599
Reaction score
1,296
Points
113
Location
Lubbock, Texas
Website
cyclestopvalves.com
A 4.4 gallon size pressure tank actually does hold 1 gallon of water. Still no where large enough without a CSV. Even with the correct 38 PSI things happen so fast with a tank that small it is probably not even filling up.
 

James Thomas

New Member
Messages
16
Reaction score
0
Points
1
Location
Missouri
A 4.4 gallon size pressure tank actually does hold 1 gallon of water. Still no where large enough without a CSV. Even with the correct 38 PSI things happen so fast with a tank that small it is probably not even filling up.
I'll have to look when I get home tonight, but I do believe it has a CSV on it right where the pipe comes out of the ground from the pitless adapter.
 

James Thomas

New Member
Messages
16
Reaction score
0
Points
1
Location
Missouri
Then I am guessing it is a 50 PSI CSV, and you need to turn the pressure switch up to 40/60 to make it work as it should.
It was set at 40/60, I had to turn it down to 40/50 because the pump would get to a little past 50psi and sit there and run, wouldn't build past 50, to shut off. I turned down the cutoff psi until the pump shut off, which landed at 50psi.
 

Valveman

Cary Austin
Staff member
Messages
14,599
Reaction score
1,296
Points
113
Location
Lubbock, Texas
Website
cyclestopvalves.com
It sounds like you have more than 1 GPM leaking somewhere in the system. The CSV will just hold 50 PSI constant and never let the tank fill and the pump shut off until you fix the leak. Try just turning off the breaker. If the pressure drops while no water is being used, you have a leak somewhere.
 

James Thomas

New Member
Messages
16
Reaction score
0
Points
1
Location
Missouri
It sounds like you have more than 1 GPM leaking somewhere in the system. The CSV will just hold 50 PSI constant and never let the tank fill and the pump shut off until you fix the leak. Try just turning off the breaker. If the pressure drops while no water is being used, you have a leak somewhere.

Ok I'm home verified i do have a CSV,
Power to the system has been off for 15 minutes with zero pressure drop. Going to keep the power off for an hour and see where we are on pressure.
 

James Thomas

New Member
Messages
16
Reaction score
0
Points
1
Location
Missouri
Also I picked up a 3/4" pipe plug if you wanted me to remove the pressure tank and plug the line, lowes was out of ball valves.
 

Reach4

Well-Known Member
Messages
38,798
Reaction score
4,412
Points
113
Location
IL
Also I picked up a 3/4" pipe plug if you wanted me to remove the pressure tank and plug the line, lowes was out of ball valves.
That was not what he had in mind. The thought was to close the valve after the pressure tank to remove the small chance that there was a leak in the house plumbing that you did not notice. There are some leaks that are not obvious.
 

James Thomas

New Member
Messages
16
Reaction score
0
Points
1
Location
Missouri
Ok went an hour with power off and had zero pressure drop in thesystem.

I adjusted the cut on/off switch back to cut on a 40psi(couldn't check the cut off because it got to 55psi and set there running) I adjusted the cutoff down to 50psi for the pumps sake.

Still have the same problem.
Valves closed pressure will sit at 50psi, as soon as a water faucet opens anywhere the pressure immediately falls to 0-5psi. As soon as the faucet closes the water climbs back to the cut off pressure (50psi)

**EDIT, I also noticed a little pressure fluttering as it was building it back up from about 15psi to 30psi then it stops.
 
Last edited:

Valveman

Cary Austin
Staff member
Messages
14,599
Reaction score
1,296
Points
113
Location
Lubbock, Texas
Website
cyclestopvalves.com
Checking the amps might help figure this out, but I am afraid the pump is just worn out. Either that or you have a leak in the pipe prior to a check valve. Either way probably going to have to pull it to see.
 