Laundry trap height, water main line vs meter size, AAV

Users who are viewing this thread

HTG

New Member
Messages
1
Reaction score
0
Points
1
Location
Renton WA
I have a legal duplex in Renton WA (UPC 2015), a 1904 house that was split into two units: the upper floor and the main floor. Building also has a basement. The unit that is being renovated is the upper, and the majority of the plumbing runs between the space between the ceiling of the lower unit and the floor of the upper in an area about 2 ft deep. My inspector is anti homeowner-doing-own-work, and wouldn't say anything other than "obtain the services of a licensed plumber", (who wants $15k??) so here I am with three questions:

1) can the laundry p-trap be located below the floor level of the upper unit where it is accessible by access panel in the floor under the washer? The vent is about 6 ft away and I have no idea how one is supposed to put a p-trap in 12" above the floor and then get a horizontal drain line across a hallway to the vent that goes through the roof. Would very much like to NOT poke another hole in my roof just for the washer vent. AAV?

2) the inspector said because I was adding a bathtub, when he returned to reinspect, he wanted to verify that the water line from meter to entry into building was 1 inch. It is 3/4" and the water meter is also 3/4" and currently comes into the basement and splits to serve upstairs unit and downstairs unit from there. Building has a single meter. If I have to upgrade to 1", do I also have to bump the water meter to 1"? The current path of the water line is from the street to the farthest away back wall of the house before it enters, and it runs under a lot of concrete, a staircase, and many other things I don't want to mess with. Can I split the water line AT the meter, and run a new 1" line for the upstairs service only, from the meter to the closest part of the building to the street, and then enter the crawl space and run it above ground through the crawl space and into the basement where it hooks up to the water line serving the upstairs unit?

3) I have to add an extractor fan in the "laundry area" and currently the extractor fans from two bathrooms (one from lower unit and the only from upper unit) join at a wye about 12 inches inside the exterior wall and then exit the building sidewall in the same combined duct. Can I add this laundry fan into the same duct exit and have all three go out the same hole? Or do I have to make a second hole next to the one already there for this third fan?
 

Reach4

Well-Known Member
Messages
38,858
Reaction score
4,428
Points
113
Location
IL
) Would very much like to NOT poke another hole in my roof just for the washer vent. AAV?
Yes.
Building has a single meter. If I have to upgrade to 1", do I also have to bump the water meter to 1"?
No.
The current path of the water line is from the street to the farthest away back wall of the house before it enters, and it runs under a lot of concrete, a staircase, and many other things I don't want to mess with. Can I split the water line AT the meter, and run a new 1" line for the upstairs service only, from the meter to the closest part of the building to the street, and then enter the crawl space and run it above ground through the crawl space and into the basement where it hooks up to the water line serving the upstairs unit?
I don't see why not. I am not a plumber.
 

Terry

The Plumbing Wizard
Staff member
Messages
29,942
Reaction score
3,459
Points
113
Location
Bothell, Washington
Website
terrylove.com
804.1 All plumbing fixtures or other receptors
receiving the discharge of indirect waste pipes shall be
approved for the use proposed and shall be of such
shape and capacity as to prevent splashing or flooding
and shall be located where they are readily accessible
for inspection and cleaning. No standpipe receptor for
any clothes washer shall extend more than thirty (30)
inches (762 mm), nor less than eighteen (18) inches
(457 mm) above its trap. No trap for any clothes
washer standpipe receptor shall be installed below the
floor, but shall be roughed in not less than six (6)
inches (152 mm) and not more than eighteen (18)
inches (457 mm) above the floor.

The trap for the washer can't be below the floor.

washer_rough_1.jpg


Since you have other venting in the home, you should be able to add an AAV for the washer.
For an AAV to work, it needs at least one vent through the roof in the system.

pipe_size_2.jpg


Bringing in 1" from the 3/4" meter helps a lot. It almost doubles the volume.
 