5 hp control box on a 3 hp pump ok?

Users who are viewing this thread

Dale Newnham

New Member
Messages
5
Reaction score
0
Points
1
Location
Desert Hills, AZ
I found that we have a 5 hp rated box when I did a capacitor check this weekend. The pump is an older 3 hp rated. This box was installed by a pump repairman last year replacing the original 3 hp control.

Will this kill our pump way faster or is it ok?

What I understand is the capacitors and overloads are rated to large for the pump.
 

Valveman

Cary Austin
Staff member
Messages
14,599
Reaction score
1,296
Points
113
Location
Lubbock, Texas
Website
cyclestopvalves.com
Yes the capacitors and overloads are rated for 5HP. The over sized capacitors won't hurt anything. But the overloads won't trip until it gets higher than like 28 amps, and a 3HP has max amps of like 14. Even this probably won't make much difference as overloads are not made to protect the pump anyway. They are designed to protect the grid power from your shorted motor. Most of the time the damage has already been done to a motor long before the overloads trip anyway. A motor can run dry and at low amps for quite a while. But when it finally gets to a critical temperature it goes south in a heartbeat. A 3HP rated for 14 amps will run a while at about 6 amps after pumping the well dry. Then it will go from 6 amps to 60 amps before you can get to the breaker to turn it off.

Real protection happens with under load and rapid cycle protection devices, as they will shut the pump off long before an overload is needed. Because by the time the overload trips, it is too little and too late.
 

Dale Newnham

New Member
Messages
5
Reaction score
0
Points
1
Location
Desert Hills, AZ
Yes the capacitors and overloads are rated for 5HP. The over sized capacitors won't hurt anything. But the overloads won't trip until it gets higher than like 28 amps, and a 3HP has max amps of like 14. Even this probably won't make much difference as overloads are not made to protect the pump anyway. They are designed to protect the grid power from your shorted motor. Most of the time the damage has already been done to a motor long before the overloads trip anyway. A motor can run dry and at low amps for quite a while. But when it finally gets to a critical temperature it goes south in a heartbeat. A 3HP rated for 14 amps will run a while at about 6 amps after pumping the well dry. Then it will go from 6 amps to 60 amps before you can get to the breaker to turn it off.

Real protection happens with under load and rapid cycle protection devices, as they will shut the pump off long before an overload is needed. Because by the time the overload trips, it is too little and too late.
 

Dale Newnham

New Member
Messages
5
Reaction score
0
Points
1
Location
Desert Hills, AZ

Thank You for getting back to me.
I won't have to put a 3 hp control back on it at that rate. We are using a pump saver on the system so we should be ok then.
 

Valveman

Cary Austin
Staff member
Messages
14,599
Reaction score
1,296
Points
113
Location
Lubbock, Texas
Website
cyclestopvalves.com
The overload in the pump saver won't do you anymore good than the one in the 5HP control box. But if the underload and rapid cycle protection in the pump saver works like it does with a Cycle Sensor, the overload should never be needed.
 

Dale Newnham

New Member
Messages
5
Reaction score
0
Points
1
Location
Desert Hills, AZ
The overload in the pump saver won't do you anymore good than the one in the 5HP control box. But if the underload and rapid cycle protection in the pump saver works like it does with a Cycle Sensor, the overload should never be needed.
Would it be advisable to change out the overloads in the box or let it ride?
 