Users who are viewing this thread

Ginahoy

Building Systems Engineer
Messages
85
Reaction score
0
Points
6
Location
Sierra Vista, AZ
I'm preparing to break ground on a my new home, which has a fully below-grade basement. A storage type water heater will be centrally located in the basement. There will be two interior sumps -- one with a sewage ejector pump for the bathroom fixtures and the other for the footer drain. I'm considering specifying a drain tile in the slab beside the water heater with a 'side arm' T&P drain pipe such that any release would flow directly into the drain tile and end up in the footer drain sump. Is this acceptable?

Basements are a rarity around here (SE Arizona) so it wasn't surprising that the first plumbing contractor I met with expressed concern about my design. First, he said he didn't think water heaters are allowed in basements. Say what?! That seems like nonsense! Next, he said the T&P drain must be routed to the outside so any activation would be noticed. I think my design accomplishes that. My takeaway is that this guy had never seen a basement before. Time to move on to another contractor.

Before I interview another plumbing sub, I want to find out if my T&P design could be a code violation. On the other hand, couldn't I simply route the T&P drain up through the floor trusses to the outside, thus saving the cost of installing a drain tile? No need for a pump since any release, by definition, would be under pressure, right?

The building site is in a rural area. The county allows owner-builders to opt out of plan review and inspections, which I have done. Still, I'm supposed to follow code, and in any case, I don't want to ask a licensed contractor to do something that would be a code violation. Clearly I need to hire a quality plumber who understands basements. If I can find one.
 
Last edited:

hj

Master Plumber
Messages
33,603
Reaction score
1,042
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
You CANNOT run the discharge line upwards. It HAS to drain to a lower elevation, even though it is under pressure. On to the floor or into a pump sump are about the only options if you want the heater in the basement.
 

Reach4

Well-Known Member
Messages
38,892
Reaction score
4,434
Points
113
Location
IL
I'm considering specifying a drain tile in the slab beside the water heater with a 'side arm' T&P drain pipe such that any release would flow directly into the drain tile and end up in the footer drain sump. Is this acceptable?
"Drain tile"??? I hope you don't plan to use terra cotta drain tiles in your floor or for anything functional. Use pvc or abs according to what is common locally.

How about calling it a floor drain? WH T+P runs to 6 inches above the floor. Floor drain below receives the water. The T+P drain is the only good use for galvanized pipe in a home IMO. Copper works too everywhere. CPVC would be allowed some places and not others.
 

Ginahoy

Building Systems Engineer
Messages
85
Reaction score
0
Points
6
Location
Sierra Vista, AZ
Sorry, by drain tile I was referring to a floor drain made of plastic with a 'strainer' plate. I never stopped to think about the origin of the term. Good to know there's no issue with my design. Thanks.
 

Crush62

Journey Level Plumber/State Certified Plmbg Instr
Messages
2
Reaction score
0
Points
1
Location
Lynnwood, Wa.
I'm preparing to break ground on a my new home, which has a fully below-grade basement. A storage type water heater will be centrally located in the basement. There will be two interior sumps -- one with a sewage ejector pump for the bathroom fixtures and the other for the footer drain. I'm considering specifying a drain tile in the slab beside the water heater with a 'side arm' T&P drain pipe such that any release would flow directly into the drain tile and end up in the footer drain sump. Is this acceptable?

Basements are a rarity around here (SE Arizona) so it wasn't surprising that the first plumbing contractor I met with expressed concern about my design. First, he said he didn't think water heaters are allowed in basements. Say what?! That seems like nonsense! Next, he said the T&P drain must be routed to the outside so any activation would be noticed. I think my design accomplishes that. My takeaway is that this guy had never seen a basement before. Time to move on to another contractor.

Before I interview another plumbing sub, I want to find out if my T&P design could be a code violation. On the other hand, couldn't I simply route the T&P drain up through the floor trusses to the outside, thus saving the cost of installing a drain tile? No need for a pump since any release, by definition, would be under pressure, right?

The building site is in a rural area. The county allows owner-builders to opt out of plan review and inspections, which I have done. Still, I'm supposed to follow code, and in any case, I don't want to ask a licensed contractor to do something that would be a code violation. Clearly I need to hire a quality plumber who understands basements. If I can find one.

You may also put a secondary T & P on the water system,(where you can access it should it fail) and install it where you can get that drain to gravity. It would be rated at 125psi/210deg. Should you experience high temp/over pressure the 125psi would discharge first. Running the T & P into a condensate pump is out of the question,too much volume should the T & P discharge..
 

Jeff H Young

In the Trades
Messages
8,931
Reaction score
2,230
Points
113
Location
92346
when we cant gravity drain the Tand P we put a pressure relief valve where it can gravity drain out in the piping above grade. and on the water heater in place of the tand p we install a watts 210 automatic gas shut off valve. of cource if you got a floor sink or drain dont need it
 

Terry

The Plumbing Wizard
Staff member
Messages
29,942
Reaction score
3,459
Points
113
Location
Bothell, Washington
Website
terrylove.com
A TEMPERATURE relief valve remote from the heater would be completely USELESS.

Not completely useless. The spring load is set for 125 PSI which will dump water if the pressure builds too high. I did a lot of plumbing in a city that wanted those 125 PSI reliefs installed.

Years later with a new inspector, things changed back to what we consider normal.
 

Jeff H Young

In the Trades
Messages
8,931
Reaction score
2,230
Points
113
Location
92346
A TEMPERATURE relief valve remote from the heater would be completely USELESS.

Pressure relief valve remote from water heater is a good thing in conjunction with a watts 210 automatic gas shut off valve at water heater. Or you need a t and p drain to an approved location.
 