Questions about new plumbing

Users who are viewing this thread

Gagecalman

Active Member
Messages
160
Reaction score
35
Points
28
Location
Baltimore, MD
Hello to all,

This is new work done by someone licensed. Permitted and inspected. IPC.

Based on the great info I've learned from this forum I have a few questions.

I am always trying to learn the correct way to do things.

The first picture is for a vanity. I know it's a tight space for the drains. Should there be long sweep 90's?

The second picture is the kitchen drain which is vented. That goes down to the basement into a sani-tee.

In the third picture that drain from the kitchen is wet venting the laundry standpipe.

In the fourth picture, the drain from the kitchen and laundry go into the stack using a sani-tee.

In the basement:

Should the sani-tees be wye combo's?

Should the laundry have its own vent?

Thanks for all of the great info!

4333 Berger 034.jpg
4333 Berger 027.jpg
4333 Berger 038.jpg
4333 Berger 041.jpg
 

Plumber01

In the Trades
Messages
108
Reaction score
17
Points
18
Location
Washington
The first picture is for a vanity. I know it's a tight space for the drains. Should there be long sweep 90's?

Yes

The second picture is the kitchen drain which is vented. That goes down to the basement into a sani-tee.

It should be a combo, not a santee.

In the third picture that drain from the kitchen is wet venting the laundry standpipe.

Not code, anywhere.

In the fourth picture, the drain from the kitchen and laundry go into the stack using a sani-tee.

Thats fine.
 

Gagecalman

Active Member
Messages
160
Reaction score
35
Points
28
Location
Baltimore, MD
"I am tying to figure out what those two "black things" are in the washer drain. Yes it MUST have its own vent."
Looks like a check valve.

It is a check valve. I was told it is code because the standpipe is below the manhole cover.

There is also one in the floor where the new plumbing was done.
 

Gagecalman

Active Member
Messages
160
Reaction score
35
Points
28
Location
Baltimore, MD
In the fourth picture, the drain from the kitchen and laundry go into the stack using a sani-tee.

plumber01 wrote: Thats fine.

I thought I read that you should use a combo there and the sani-tee should be used for a trap arm.
So can either be used and is one better than the other?
 

Gagecalman

Active Member
Messages
160
Reaction score
35
Points
28
Location
Baltimore, MD
In the fourth picture, the drain from the kitchen and laundry go into the stack using a sani-tee.

plumber01 wrote: Thats fine.

I thought I read that you should use a combo there and the sani-tee should only be used for a trap arm.
So can either be used and is one better than the other?[/QUOTE]

Can someone help me with this please?
 

hj

Master Plumber
Messages
33,603
Reaction score
1,042
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
If it is a check valve, there is almost NO possibility that it would operate properly, because the washer lint will coat the seat and flapper to prevent sealing. If it is an "inline spring check" there will not be enough pressure to open it before the drain overflows. If a trap arm does NOT have its own vent, then a sanitary tee is REQUIRED. In this case there is a vent so any fitting can be used.
 

Gagecalman

Active Member
Messages
160
Reaction score
35
Points
28
Location
Baltimore, MD
If it is a check valve, there is almost NO possibility that it would operate properly, because the washer lint will coat the seat and flapper to prevent sealing. If it is an "inline spring check" there will not be enough pressure to open it before the drain overflows.
If a trap arm does NOT have its own vent, then a sanitary tee is REQUIRED. In this case there is a vent so any fitting can be used.

Thanks for the reply. It's strange but I was told that the check valve is required here in Baltimore City.

I assumed this a branch line due to the kitchen drain coming down into it and wet venting the utility sink (which is wrong).
If it is a branch can any fitting be used where it connects to the stack?
 

Gagecalman

Active Member
Messages
160
Reaction score
35
Points
28
Location
Baltimore, MD
I am trying to make sure I understand how to use the correct fittings.

If that line is a vented trap arm or it is a branch line a sani-tee or a combi can be used?

So can either be used and is one better than the other?

Thanks again for you patience!
 

Kreemoweet

In the Trades
Messages
754
Reaction score
66
Points
28
Location
Seattle. WA
A santee is acceptable anywhere for changing drain flow direction from horizontal to vertical. So are other
fittings. Santees are better because they are cheaper than the others, and are easier to use in tight quarters.
 