TPR oddly piped - code?

Users who are viewing this thread

Stephenson

Member
Messages
164
Reaction score
2
Points
18
Location
Florida and Virginia
Hi All,

Just replaced a gas water heater with electric - short story of why convert to electric:
1. Gas in this area (Pensacola, FL) is very expensive compared to most areas
2. About $18 a month of overhead fees to maintain the access
3. Gas Water Heater is the only gas appliance (other than useless fireplace)
4. Electricity is more fairly priced here
5. Electric company paid for the new electric water heater

I knew the gas heater had an oddly piped TPR pipe, but didn't "test" it until I installed the new heater - test in this case was simply leaving the vent open a bit too long during the initial water fill.

The photo shows the story - the pipe runs into the wall just under the wood floor of the air handler so ya can't see were is goes from there. I believe it simply dumps into the area as the damp concrete shows just outside the wall ...

Given this is an accurate assessment, would it pass code? (I could find no other examples of this)

Thanks!

HWH Photo to Post.jpg
 
Last edited by a moderator:

Cacher_Chick

Test, Don't Guess!
Messages
5,458
Reaction score
213
Points
63
Location
Land of Cheese
I would think that there is a drain for the evaporator on the HVAC unit which the pipe is or was plumbed to.
 

Stephenson

Member
Messages
164
Reaction score
2
Points
18
Location
Florida and Virginia
Cacher,

Yeah - thought that originally, as well, but the HVAC condensate drain is completely independent ... note how the water has seeped through/under the veritcal concrete area ... was larger immediate following the "venting" of lots of water behind it ... has gotten smaller with time.
 

Cacher_Chick

Test, Don't Guess!
Messages
5,458
Reaction score
213
Points
63
Location
Land of Cheese
Cacher,

Yeah - thought that originally, as well, but the HVAC condensate drain is completely independent ... note how the water has seeped through/under the veritcal concrete area ... was larger immediate following the "venting" of lots of water behind it ... has gotten smaller with time.

Where I am it is an accepted practice to allow the discharge to go to the floor if there is a drain for it (common in a basement). In warmer climates, discharging out aa sidewall to the outdoors is pretty common.
My preference is to have is discharge to the location where is will be noticed because any discharge from it IS a sign of a problem that needs to be addressed in short order.
 

hj

Master Plumber
Messages
33,600
Reaction score
1,037
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
To be code compliant, the end of the pipe MUST be visible so any leakage is visible and to verify that no one has tampered with the outlet by capping or plugging it.
 

Stephenson

Member
Messages
164
Reaction score
2
Points
18
Location
Florida and Virginia
To be code compliant, the end of the pipe MUST be visible so any leakage is visible and to verify that no one has tampered with the outlet by capping or plugging it.

Yep, think so, too ...here's a quick summary article, but net is that mine needs to be cut where it turns to go into the wall, then extended to not more than 6" above the floor ...water heater is in ground level concrete floored garage, so don't need a drain.

https://www.nachi.org/tpr-valves-discharge-piping.htm

Concur?
 

WorthFlorida

Clinical Trail on a Cancer Drug Started 1/31/24. ☹
Messages
5,726
Solutions
1
Reaction score
982
Points
113
Location
Orlando, Florida
That drain line may go under the garage floor, maybe in the same trench with the A/C drain pipe to somewhere outside but it should never come to the surface or drip out of the wall. I would cut the pipe and bring it to about 8 inches off the garage floor. Both of my homes in Palm Beach and Orange counties the water heaters are in the garage with the this pipe right at the base of the water heater. Like it was mentioned above, you would want to see any discharge from the TPR valve should a problem arise.

You're right about switching to electric. Florida has fairly low prices for electric power. Electric water heaters are quite reliable and last longer than gas units. I estimate that even when my kids were living at home that the water heater may added no more than $80 a month to the electric bill. Right now with just my wife my electric bill for my Palm Beach County home average $150 a month and that was with the AC running most of the year and a pool pump running average 5 hours a day, 8-10 hours in the summer. I sold that home and now I live in Orange County and the electric usage is less, mainly because this newer home is better insulated and no pool.
 

Stephenson

Member
Messages
164
Reaction score
2
Points
18
Location
Florida and Virginia
Finally got to the bottom of this ...

First, the TPR valve went down through the slab to somewhere unknown ...I cut it off and extended it to about 6 inches off the floor ...will still be a mystery, I guess.

Second ...found the leak ... Opened up the wall and found a bad sweat joint at a 90 off the hot water out line with back side of the joint with no solder ...looked like it had been tiny leak for years ...just wet enough to form a drop every few minutes ...cut it out and repiped.
 