Issue with new water heater

Users who are viewing this thread

Mayers

New Member
Messages
3
Reaction score
0
Points
1
Location
North Versailles, Pennsylvania
Hello everyone,

I recently installed a new electric water heater. The pressure relief valve keeps popping off non stop within seconds of water starting to fill the tank. Please note there is no expansion tank installed and there is no pressure reducing valve installed on the plumbing system. Also no back flow device.

I checked the pressure coming into the house and it's averaging around 130 to 140 PSI. My understanding is this is high and a pressure reducing valve would fix this. Would this also be the reason the pressure relief valve on the water heater is popping or could it have shipped with a bad pressure relief valve?

Should I go with an expansion tank first or the pressure reducing valve?
 

Smooky

In the Trades
Messages
2,299
Reaction score
152
Points
63
Location
North Carolina
Most T&P valves are designed to open at 150 psi. If it is opening at a pressure lower than that, it could be a faulty valve. The pressure is very high so I would recommend installing a pressure regulator and expansion tank.
 
Last edited:

Dj2

In the Trades
Messages
2,611
Reaction score
258
Points
83
Location
California
Quote: "Should I go with an expansion tank first or the pressure reducing valve?"

You want to stabilize and reduce your in house pressure to between 50 and 80 first.
 

Reach4

Well-Known Member
Messages
38,798
Reaction score
4,412
Points
113
Location
IL
Should I go with an expansion tank first or the pressure reducing valve?
The PRV goes first, and the thermal expansion tank goes farther in. The tank is often placed near the water heater.
 

Mayers

New Member
Messages
3
Reaction score
0
Points
1
Location
North Versailles, Pennsylvania
Thank you very much for your replies. I'll go home depot in the morning and get the PRV and expansion tank. :)

BTW my understanding is most PRV have a built-in backflow device? Is this correct?
 

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,770
Reaction score
1,190
Points
113
Location
New England
If a PRV has a bypass valve, it won't open until the home pressure exceeds the supply pressure, which, kind of defeats the purpose of a PRV to keep the pressure stable. Without an ET, the pressure will cycle high enough to either return via a bypass, if present and working, or get high enough to cause the safety T&P valve to open.

While you may not have installed a check valve or had a PRV, it is quite possible that the utility company may have installed one in the line to your house. This is done to help protect their supply in case some pollution might try to push back into their system. IOW, a bypass may not work, since many utility companies are installing check valves, or will be as they get around to upgrading things. You should not rely on a bypass in a PRV to do much of anything.
 
Top
Hey, wait a minute.

This is awkward, but...

It looks like you're using an ad blocker. We get it, but (1) terrylove.com can't live without ads, and (2) ad blockers can cause issues with videos and comments. If you'd like to support the site, please allow ads.

If any particular ad is your REASON for blocking ads, please let us know. We might be able to do something about it. Thanks.
I've Disabled AdBlock    No Thanks