Have a dual bowl kitchen sink with disposal centered beneath a bay window, which prevents me from using a traditional vent as the window is 40" above FFF so I cannot make 6" above the rim before the vent would need to turn horizontal. Seems the only options are AAVs (no thanks) or a loop vent.

I cannot use a dual fixture fitting to serve both sinks because there is an electrical outlet blocking the central vent. Also, due to a thick old foundation wall immediately below the kitchen, there is no room for the usual below-floor horizontal leg of the vent or for that matter the 45 elbows and wyes that connect the loop to the drain.

Shown below is my proposed solution.

Questions:
1. Is a loop vent permitted in other (non-island) installations?
2. Can this all be enclosed in an exterior wall?
3. OK to have the horizontal vent tie-in above the floor?
4. OK to have the drain and loop connect to the 2" drain using Sanitary tees on the flat?
5. OK to have the horizontal portion at the top of the loop vent instead of the usual 90 degree elbow peak?

Thanks in advance and I'd appreciate any simpler or superior alternatives.

kitchen vent.jpg
 

hj

Master Plumber
Messages
33,602
Reaction score
1,038
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
My experience has been; Yes to #1,2, and 3. NO, to #4 and 5. The "central vent" does NOT have to be in the exact center. Why the "drip leg" on the 2" main vent? You also need a cleanout on the drain line itself, not just the vent.
 
Last edited:

douglasgb

New Member
Messages
7
Reaction score
0
Points
0
Location
Baltimore
Website
www.gauck.com
Thank you for your reply to this and to all the other discussions I've been reading.

The drawing shows just part of the main vent (and waste) as it comes up from the basement and continues upward (no drip leg).

As you point out I could use an off-center dual fixture fitting and thus have a single vent and do a traditional loop vent from there... solving #5. Will also add a cleanout.

Still stuck on #4 though. Would Sanitary tees on the flat be allowed if they were just drains and not part of a loop vent?

The window is 68" wide and the sink is right in the middle... a 45 degree vent won't clear the window and a dirty arm would be pushing length...and I was hoping to retain individual traps for each bowl.

Racking my brains here...
 

Asktom

Member
Messages
745
Reaction score
32
Points
18
Location
Victor, MT
Simple is best. If you can use one trap and a dirty arm 42" or less I think that is the way to go.
 

douglasgb

New Member
Messages
7
Reaction score
0
Points
0
Location
Baltimore
Website
www.gauck.com
Simple is best. If you can use one trap and a dirty arm 42" or less I think that is the way to go.

I agree that simplest is best. But I just measured and the dirty arm would be more than 42". I don't think there is a perfect answer, so as much as I dislike doing so, I think it's going to come down to picking the lesser of all evils... dirty arm would be too long (window width), loop vent can only be tied to the drain with san tees on the flat (foundation wall), and vertical vent will turn at 40" (window). I'm leaning towards this last choice as the best of what seems possible.
 

hj

Master Plumber
Messages
33,602
Reaction score
1,038
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
The sanitary tees are illegal WHEN they are part of a drain, it has nothing to do with being part of a loop vent. And since the "main vent" also serves the basement yours would have to tie into it at least 42" above the floor. Otherwise it becomes an "alternate drain path" if the regular horizontal drain plugs up.
 

douglasgb

New Member
Messages
7
Reaction score
0
Points
0
Location
Baltimore
Website
www.gauck.com
I sure do appreciate everyone's time and thoughts on this.

Here in Baltimore City we are under NSPC 2009. In regards to vent, 12.6.2 states vents shall rise min of 6" above flood level of the rim of the fixture "before connecting to another vent" but has two exceptions:

-loop vents for island sinks
-horizontal portions of a vent below the floor level that a) have the invert of the horizontal portion of the vent is at or above the centerline of the horizontal waste pipe, b) drains by gravity back to the drain, and c) has clean outs so blockages in the below-flood portion can be cleared into the drain.

Reading closely, I can do #2! It seems to allow for my strongly preferred and simple dual drain setup:
simple.jpg
Drains are all 2" but turn 90 to be horizontal just below the floor and then 45 into wyes into the 2" drain to the stack.

I'd rather not do the loop but this is what it would look like:
loop.jpg
 

Asktom

Member
Messages
745
Reaction score
32
Points
18
Location
Victor, MT
In your top drawing the vents of the two traps are tied together too low. If one side clogs up there is an alternate way for it to drain - via the vent to the other side.
 

hj

Master Plumber
Messages
33,602
Reaction score
1,038
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
There is absolutely no benefit to using the loop in the second drawing if you can install it like the upper one. Since the two vents are tied together right under the window framing, the sinks would be full of water before the vent could become a "secondary drain". Therefore, someone would be aware it was happening, (unless they liked having a sink full of water all the time), and the only side effect would be that that sink could not overflow. But, if you can install the drains as in your second drawing, with a "double fixture fitting", WHY would you not do so with the first drawing and eliminate the second drain riser and vent? That would also eliminate any problems caused by the two vents. Or do you have some kind of compulsion that makes you want to have two risers in the wall, regardless of what they are? Another possibility, but it might be beyond the scope of a DIYer might be to run the single vent in 1 1/2", use 1/6 bends to angle the vent, starting just above the sink's sanitary tee, and adjust the location of the riser so the angled vent clears the lower left corner of the window. This is my method quite often when I have a situation like that, such as in my current residence. Depending on the specifics of your location, I might also angle the combos up and into 45s just below the floor, to make a better flowing drain.
 
Last edited:

douglasgb

New Member
Messages
7
Reaction score
0
Points
0
Location
Baltimore
Website
www.gauck.com
..."sink full of water"... ..."some kind of compulsion"... Have you been in contact with my wife? She hates it when I let the pots soak.

I much prefer the non-loop configuration and will go with that, including rolling the combos as much as I can and using 45s as you suggest. The reasons in my head for two risers are 1) lowest likelihood that one sink would ever flow into the other; 2) the holes in the framing already exist (this is all to fix a previous non-vented install); 3) there is a stud just to the left of the right hand riser; 4) vague feeling that combining them later with 14" between the tees would yield better capacity/lower likelihood of clogs than doing so with the dual fixture, and would outweigh the potential problems with two vents. Reasons #2 and #3 are obviously not a big deal and that last one may be pure voodoo.

I thought 45 degrees was the delineation between what's considered horizontal versus vertical, and since I cannot clear the LL corner of the window at 45 degrees, I sent the vent up and then over. If you believe a continuous slope from above the sanitary tee to above 42", even if it's a shallow angle (say 22.5 degrees) is better, I can do that.

Final (?) version (although looking at it, it does make two risers seem ridiculous):
final.jpg

Transition from sloped to vertical vent would be above 42". Need cleanouts on the vent(s)?
 

hj

Master Plumber
Messages
33,602
Reaction score
1,038
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
No cleanouts on the vents, but one on the right hand drain line below the sink's tee. Doing it "twice" is "dumb" as you have seen once it is drawn out. If the drain plugs up it will be in the horizontal section, and probably past the second tee, so the two sinks will still flow into each other. All you are doing is making a lot more work for yourself.
 
Last edited:

douglasgb

New Member
Messages
7
Reaction score
0
Points
0
Location
Baltimore
Website
www.gauck.com
I'm going to turn both vents 60° at the same elevation above the tees and send them over past the window, and then turn them up as soon as possible (was not thinking clearly last night... they don't need to be above 42" before going vertical). Then once they are higher than 42", wye them together, go up a bit more and the turn 90° to tee them into the main vent. Cleanouts are the black circles. I finally like it. Any thoughts?

finalfinal.jpg

Edit: just read your edit... thinking....
 
Last edited:

Tom Sawyer

In the Trades
Messages
3,625
Reaction score
34
Points
48
Location
Maine
I'm going to turn both vents 60° at the same elevation above the tees and send them over past the window, and then turn them up as soon as possible (was not thinking clearly last night... they don't need to be above 42" before going vertical). Then once they are higher than 42", wye them together, go up a bit more and the turn 90° to tee them into the main vent. Cleanouts are the black circles. I finally like it. Any thoughts?

View attachment 22240

Edit: just read your edit... thinking....


Just run 3" under the sink and waste stack vent it
 

douglasgb

New Member
Messages
7
Reaction score
0
Points
0
Location
Baltimore
Website
www.gauck.com
It's all over but the shouting:

IMG_5702.jpg

The vents go off at 67.5 degrees as those are street 45s + 22.5s into the 1.5x2x2 sanitary tee. The drains turn 90 just under the floor and then 45 into wyes that I rolled almost to 45 degrees so I feel pretty good about the whole thing. Thanks again for all the responses.
 

Tom Sawyer

In the Trades
Messages
3,625
Reaction score
34
Points
48
Location
Maine
It's all over but the shouting:

View attachment 22277

The vents go off at 67.5 degrees as those are street 45s + 22.5s into the 1.5x2x2 sanitary tee. The drains turn 90 just under the floor and then 45 into wyes that I rolled almost to 45 degrees so I feel pretty good about the whole thing. Thanks again for all the responses.

You might feel pretty good about it but the inspector won't. They need to rise what a minimum of 45 degrees. Nor will he be pleased with the holes / notches you cut in the studs.
 

hj

Master Plumber
Messages
33,602
Reaction score
1,038
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
quote; They need to rise what a minimum of 45 degrees.

Unless the inspector is "anal retentive" and has the I.Q. of a turnip, he will know that ANY angle is NOT horizontal. I have been doing it this way for over 60 years and have NEVER had an inspector say, "Sorry, that is not a 45 degree angle so you have to change it."
 

Tom Sawyer

In the Trades
Messages
3,625
Reaction score
34
Points
48
Location
Maine
quote; They need to rise what a minimum of 45 degrees.

Unless the inspector is "anal retentive" and has the I.Q. of a turnip, he will know that ANY angle is NOT horizontal. I have been doing it this way for over 60 years and have NEVER had an inspector say, "Sorry, that is not a 45 degree angle so you have to change it."

Well I just happened to have a meeting this afternoon with about a dozen local inspectors. Showed them the picture and all but one said they'd fail that on both counts. Maybe I should move out west where apparently the code is variable lol
 

hj

Master Plumber
Messages
33,602
Reaction score
1,038
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
quote; they'd fail that on both counts

You mean because they are both "anal retentive" AND have the I.Q. of a turnip?

You might only have to move to the Chicago area, because that was where I first started doing it, without ANY problems, but maybe we just had better inspectors, not guys who started as contractors and went broke, then became inspectors without getting any smarter. The reason for the "45 degree angle", ( and it is something most people can understand and relate to, as opposed to "60 or 67 1/2 degrees" from the vertical"), is STRICTLY for drainage purposes and ANY angle, other than horizontal, accomplishes that. But I still say that THIS installation was a lot of work, and money, with NO benefits compared to the easier ways of doing it.
 
Last edited:
Top
Hey, wait a minute.

This is awkward, but...

It looks like you're using an ad blocker. We get it, but (1) terrylove.com can't live without ads, and (2) ad blockers can cause issues with videos and comments. If you'd like to support the site, please allow ads.

If any particular ad is your REASON for blocking ads, please let us know. We might be able to do something about it. Thanks.
I've Disabled AdBlock    No Thanks