wiring a hot tub

Users who are viewing this thread

ShockHazard

New Member
Messages
50
Reaction score
0
Points
0
Location
North East Pennsylvania
60 amp GFCI breaker, 4 wire
Disconnect outside on the house wall.

1) Can I legitamatly put a 120 outlet near this disconnect, powered by one of the two leads coming from the GFCI?
2) Does this outlet need to be, itself a GFCI?
3) Should the disconnect be a breaker?
4) If so, what amperage?

Thanks in advance.
 

Glennsparky

New Member
Messages
22
Reaction score
0
Points
0
Location
Oviedo, FL near Orlando
1) Can I legitamatly put a 120 outlet near this disconnect, powered by one of the two leads coming from the GFCI? .
Not without a 15 or 20 amp breaker to protect the outlet. And not if the spa instructions say "dedicated circuit."
2) Does this outlet need to be, itself a GFCI?.
It needs to be GFCI protected. If the 60A GFCI feeds a panel. That panel can have a normal breaker that feeds a normal receptacle. But that's a bad design.
3) Should the disconnect be a breaker?.
It's not necessary if the 60A GFCI was used earlier in the circuit.

A better design is to use a four or more space panel where the disconnect would go. Do a load calculation and feed that panel with the correct wires. Put a normal breaker in the main panel to protect those wires. Then use the 60A GFCI in the subpanel. It's also the disconnect. In the subpanel use a normal breaker to feed a GFCI receptacle.

This way when 120V loads nuisance trip the GFCI there will be less walking and the spa wont shut off.
 

ShockHazard

New Member
Messages
50
Reaction score
0
Points
0
Location
North East Pennsylvania
Ok, so pulling a 110 out of this 220 setup is okay if it has it's own breaker?

Second response: Lets say I have this 110 outlet on it own 15 amp breaker, and the whole shabang is gfci protected at the panel. Is is gfci protected, even thought the gfci breaker is predicting a 220 volt load? I'd never try it, I'm simply curious from a design perspective.

Third response: Makes sense, but is there an issue with a non-gfci circuit running outside, then underground as it travels to this disconnect?

I never run anything outdoors without a gfci breaker, just as a matter of habit.
 

ShockHazard

New Member
Messages
50
Reaction score
0
Points
0
Location
North East Pennsylvania
Lets say I did decide to have a 60 amp breaker in the (primary) box, and another breaker as a disconnect.
What amperage should it be, or should it simply never be?

Is there ever an example of a sub panel having only one breaker?
 
Last edited by a moderator:

hj

Master Plumber
Messages
33,600
Reaction score
1,037
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
The big question is what is connected to the 60 amp breaker, and can it be converted to a sub panel? You can have as many, or few, breakers in a sub panel as you need. ANY breaker can be the size required for its load, as long as the load's wire capacity is not exceeded.
 

Glennsparky

New Member
Messages
22
Reaction score
0
Points
0
Location
Oviedo, FL near Orlando
Ok, so pulling a 110 out of this 220 setup is okay if it has it's own breaker?
yes
Second response: Lets say I have this 110 outlet on it own 15 amp breaker, and the whole shabang is gfci protected at the panel. Is is gfci protected, even thought the gfci breaker is predicting a 220 volt load? I'd never try it, I'm simply curious from a design perspective.
yes. Happens all the time. Most spas have 120 and 240 volt equipment. For many it's a 240V pump and 120V blower.
Third response: Makes sense, but is there an issue with a non-gfci circuit running outside, then underground as it travels to this disconnect?
nope, as long as all other issues are to code.
 

Glennsparky

New Member
Messages
22
Reaction score
0
Points
0
Location
Oviedo, FL near Orlando
Lets say I did decide to have a 60 amp breaker in the (primary) box, and another breaker as a disconnect.
What amperage should it be, or should it simply never be?
Any amperage. Below 60A as long as it can still serve the load. Above 60A and it's short circuit interrupt function is superfluous.

Is there ever an example of a sub panel having only one breaker?
Every portable spa I've ever installed. Two space panel, one double pole GFCI breaker.
 