What is Cause of High Current in New Submersible Pump

Users who are viewing this thread

petegerster

New Member
Messages
5
Reaction score
0
Points
0
Location
New jersey
With a great deal of help from this forum I replaced my jet pump with a submersible. We now have a system that at least from the standpoint of taking a shower is much better than the previous system which we used for almost 40 years. However there is one problem. The current being drawn by the pump motor is 5.1 amperes and the FLA specification is 3.7 amperes.

Here is what I believe to be the pertinent information:

MANUFACTURER SPECIFICATIONS
Goulds Pump - 7GS05422C Motor - M05422-50C211
There is a ball valve on the pump outlet pipe as it enters the basement which restricts the flow so that the outlet head does not drop below a value which would allow the pump to operate outside its design volume.
Motor is 2 wire 230 volts - thermally protected.
Full Load Amps spec - 3.7A
SF Amps spec - 4.7A
Winding resistance spec - 4.6 to 5.6 ohms

TEST DATA ON MY SETUP.
Voltage at pressure switch during pump operation - 242 volts
Current - 5.1A
Total dynamic head at pump outlet - 200 feet
Volume produced by pump - 8 GPM
Expansion tank and house distribution system disconnected. One faucet open.
Resistance of motor leads including 340 ft of 12 gauge copper conductor - 5.3 ohms (measured at pressure switch)
Resistance from motor leads to ground - greater than 30 megohms (measured at pressure switch)

After I first installed the system I ran the pump for about 20 minutes under the conditions specified above. I was not keeping careful track of time. I was trying to get the water to run clear. I stopped the test because the water stopped coming out which I interpreted as the pump having emptied the well, so I immediately shut off power to the pump to avoid damage to it. (I have not yet installed a low water shut-off.) In my hurry to shut the pump off I did not note whether it was still running. It may have cut out on high temperature The column of water in the well is about 150 gallons. I turned the power back on. The pump restarted and continued to pump normally. I am unsure how long it was powered off, perhaps 5 - 10 minutes.

Not understanding the problem I hesitate to run the pump for long periods although when I disinfected the well the pump seemed to operate normally, except for the high amps, during the chlorine purge phase.

I have thought about what might be happening and have come up with two possible reasons for the high current. There are probably others which with my limited knowledge I have overlooked.

(1) A faulty pump. This seems unlikely.

(2) This is more complicated. Before installing the pump, I fabricated a shroud from 4" thin wall sewer pipe as described elsewhere on this forum, and attached it to the pump using 2 stainless hose clamps around the pump about 4" above the intake. I tightened the clamp screws quite firmly using a socket wrench. At the time I felt uneasy about doing this, but I couldn't think of any other way to attach the shroud to the pump, and I could not find anyone advising against it. The clamps go over what Goulds calls the cable guard which is a longitudinal metal housing covering the wires going past the pump to the motor.

What may have occurred is that the cable clamps by putting force on the cable guard has distorted the pump body such that it is causing interference between the impeller and the fixed housing of the pump.

Would anyone please suggest other possible causes of the over-current problem, or if you think the clamps are the source then how does one attach the shroud to the pump? I thought of putting the clamps very near the motor end of the pump housing, but I was concerned that the shroud, when squeezed down, would obstruct the suction of the pump.

Thank you for any insights you might provide.
 

Valveman

Cary Austin
Staff member
Messages
14,626
Reaction score
1,301
Points
113
Location
Lubbock, Texas
Website
cyclestopvalves.com
My book shows a 1/2 HP, 240V, 2 wire submersible is good to 6 amps. They always load subs heavy, so max amps are the norm. Don't think you have anything to worry about.
 

petegerster

New Member
Messages
5
Reaction score
0
Points
0
Location
New jersey
My book shows a 1/2 HP, 240V, 2 wire submersible is good to 6 amps. They always load subs heavy, so max amps are the norm. Don't think you have anything to worry about.


Dear Valveman,
Thank you for your prompt response.

May I assume from your not having commented on it, that my concern for the cable clamps inducing a slight interference between the housing and the impeller is not valid? If this were to occur it would increase the torque requirement of the pump and the current required by the motor. My thought was that the cable clamp on the cable guard might cause the pump housing to go slightly out of round. I have never seen the innards of a submersible pump so I have no way to judge the stiffness of the housing or the clearance between the housing and the impeller.

I will try not to worry about it, but I am a worrier by nature. Thanks again.
 

Valveman

Cary Austin
Staff member
Messages
14,626
Reaction score
1,301
Points
113
Location
Lubbock, Texas
Website
cyclestopvalves.com
200’ of “Total Dynamic Head” is the same as a water level at about 85’ and 50 PSI, at which that pump will deliver 8 GPM just fine.

You will strip the worm gear out of the hose clamp before it gets tight enough to crush anything. But if it did, it would crush the wire on the outside of the pump before it hurt the pump itself.

The shroud is so good for the motor that it was well worth your efforts.
 

LLigetfa

DIYer, not in the trades
Messages
7,502
Reaction score
577
Points
113
Location
NW Ontario, Canada
An impeller pump is not positive displacement so additional head usually results in less current draw, not more.
 

petegerster

New Member
Messages
5
Reaction score
0
Points
0
Location
New jersey
I would like to thank everyone who responded to my post, especially valveman, whose advice I plan to follow.
 

Ballvalve

General Engineering Contractor
Messages
3,581
Reaction score
45
Points
48
Location
northfork, california
I'll add that using pull ties of nylon is safer. And when you use a ton of them to tie the wire to the drop pipe, and you leave them LONG, they become standoffs that cant catch anything.
 
Top
Hey, wait a minute.

This is awkward, but...

It looks like you're using an ad blocker. We get it, but (1) terrylove.com can't live without ads, and (2) ad blockers can cause issues with videos and comments. If you'd like to support the site, please allow ads.

If any particular ad is your REASON for blocking ads, please let us know. We might be able to do something about it. Thanks.
I've Disabled AdBlock    No Thanks